[RE-wrenches] SolarEdge inverter blowing fuses
Jason Szumlanski
jason at floridasolardesigngroup.com
Mon Nov 1 20:43:50 EDT 2021
See attached image. Notice the discoloration on the top of the left fuse.
It's always the same thing, same place.
Jason
On Mon, Nov 1, 2021, 8:30 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> I should also mention that it has nothing to do with ambient heat. This
> has occured in all seasons and with disconnects in direct sunlight on a
> south wall and disconnects in air conditioned garages.
>
> It's just a garbage product. We switched to Square D for 60A D222NRB
> fusible disconnects and are also using their 100A circuit breaker
> enclosures which are cost effective. The D223NRB is also a good fusible
> disconnect, but pricey.
>
> Jason
>
>
> On Mon, Nov 1, 2021, 8:24 PM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>> It's the disconnect. We had dozens of this subpar disconnect design fail
>> on Enphase systems. The 2 Pole has the same issue.
>>
>> GE gave us some nonsense answer that it's General Duty and not designed
>> for continuous high power. Even 40A combined Enphase systems will blow a
>> 60A fuse.
>>
>> What you will find is the fuse will blow on one side and then
>> replacements will blow at decreasing intervals until it blows daily. Our
>> experience is the left side (of the 2-pole) is far more problematic for
>> some odd reason. It's not the fuse brand either.
>>
>> I believe the design fault is how the blades only hit a single contact on
>> one side when they close. The Square D alternative has the blade slipping
>> between two contacts.
>>
>> Sadly we have had to replace so many of these and most are supply side
>> interconnections, which make it tricky and expensive.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>>
>>
>>
>> On Mon, Nov 1, 2021, 4:26 PM Dave Tedeyan <dave at sungineersolar.com>
>> wrote:
>>
>>> Hi All,
>>>
>>> I am servicing a system that keeps blowing fuses on the AC side,
>>> although it
>>> appears that everything is sized correctly. It is a SolarEdge
>>> SE11400A-US inverter.
>>> Max continuous output current is 47.5A x 1.25 = 59.4A. There is a GE
>>> TG3222R
>>> 60A AC disconnect, and it is wired up with #6 THHN wire. The terminals
>>> were tight
>>> and there was no evidence of arcing or burning in the past. This is
>>> indoors, and not
>>> exposed to sunlight. No extra conductors are in the conduit.
>>>
>>> But they say that they need to replace a fuse roughly once per month.
>>> Has anyone
>>> seen this before? Could there be some kind of fault in the inverter
>>> itself that
>>> occasionally induces extra current? Is there any way to tweak the
>>> settings so that it
>>> actually produces a bit more than 11.4kw? I appreciate your thoughts.
>>>
>>> Cheers,
>>> Dave
>>>
>>> --
>>> [image: Logo] <https://www.sungineersolar.com/>
>>> Dave Tedeyan, P.E.
>>> Owner | Sungineer Solar
>>> p: he | him | his
>>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>>> c: (607) 288-2898
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211101/73c5be0c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20210602_134215-resized-1024.jpg
Type: image/jpeg
Size: 321000 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211101/73c5be0c/attachment.jpg>
More information about the RE-Wrenches
mailing list