[RE-wrenches] SolarEdge inverter blowing fuses
Lloyd Hoffstatter
lloyd at sunstruckconsulting.com
Mon Nov 1 16:45:46 EDT 2021
Dave,
My first thought would be a small nick in wire insulation going to ground, causing the fuse to fail over time.
We had a similar situation with a much larger system where the culprit was hard to noticeā¦
Best regards,
Lloyd
Lloyd Hoffstatter
Sunstruck Consulting
Sent from Mail<https://go.microsoft.com/fwlink/?LinkId=550986> for Windows
From: Dave Tedeyan<mailto:dave at sungineersolar.com>
Sent: Monday, November 1, 2021 4:26 PM
To: RE-wrenches<mailto:re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] SolarEdge inverter blowing fuses
Hi All,
I am servicing a system that keeps blowing fuses on the AC side, although it
appears that everything is sized correctly. It is a SolarEdge SE11400A-US inverter.
Max continuous output current is 47.5A x 1.25 = 59.4A. There is a GE TG3222R
60A AC disconnect, and it is wired up with #6 THHN wire. The terminals were tight
and there was no evidence of arcing or burning in the past. This is indoors, and not
exposed to sunlight. No extra conductors are in the conduit.
But they say that they need to replace a fuse roughly once per month. Has anyone
seen this before? Could there be some kind of fault in the inverter itself that
occasionally induces extra current? Is there any way to tweak the settings so that it
actually produces a bit more than 11.4kw? I appreciate your thoughts.
Cheers,
Dave
--
[Logo]<https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com<http://www.sungineersolar.com/>
c: (607) 288-2898
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211101/8ff4c6a6/attachment.htm>
More information about the RE-Wrenches
mailing list