[RE-wrenches] DC Rating of Square D QO?
Ray Walters
ray at solarray.com
Mon Oct 25 21:55:47 EDT 2021
I've got some old systems running the QO breakers at 48 v nominal, but
the Voc of the array could be over 80. Never an issue, but I agree just
swap out that load center, since its that old. Midnite has good stuff.
If you're just running to a an FM80 or similar with 150 v limit, their
regular breakers are 150 vdc rated. I only use the 300 v rated breakers
with the new FM 100 that can take 300 vdc.
Ray Walters
Remote Solar
On 10/25/2021 6:45 PM, Chris Sparadeo wrote:
> Hi Jeremy,
>
> According to the QO cut sheet the answer is 48VDC:
>
> https://download.schneider-electric.com/files?p_Doc_Ref=0730CT9801
>
> My guess is that your string voltage would be much greater than that.
> Not sure your exact application, but for the slight added cost, I
> would definitely suggest using a reputable NEMA3R combiner/disco with
> 300VDC breakers and throwing away the ancient load center.
>
>
>
>
> On Mon, Oct 25, 2021 at 8:30 PM Jeremy Rodriguez
> <allsolarjeremy at msn.com> wrote:
>
> Hello
> Does anyone have a definitive answer to the DC rating of the QO
> circuit breakers? I’ve got a potential client with an existing
> AC load center (>20 yrs) being used for his array combiner.
> He’s looking to add to the array, with modules that are higher
> voltage of course.
> Thanks in advance.
>
> Jeremy Rodriguez
> Solar Installation / Design Expert
> All Solar, Inc.
> 1453 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work,
> try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211025/1b13fbd0/attachment.htm>
More information about the RE-Wrenches
mailing list