When installing a system with more than two Encharge 10 batteries, a
separate load center needs to be used to combine AC battery output. It
would just require two 2-pole breakers in a MLO panel. But I believe both
of those breakers would need to be fastened down.

If anyone is doing this, are you aware of a small four-space panel where
you can put a hold down kit in both 2-pole breakers? Model number would be
greatly appreciated. My Eaton rep claims that their breaker hold down kit
only works in panels 150A and greater and only one space is provided for a
hold down kit. Other than that, you would have to go to a panelboard with
bolt on breakers. That doesn't sound right to me.



Jason Szumlanski
Florida Solar Design Group