Hi William - You raise a great question - can you install 600 VDC modules
on a 1000 VDC SolarEdge system? Of course the DC optimizer output circuit
would need to be rewired with 1000 VDC wiring and connectors, but I think
the answer is "yes." According to this article
<https://www.solaredge.com/sites/default/files/application_notes_string_combiners_na.pdf>,
"In a SolarEdge system, the PV modules are isolated from the DC output
circuit by the power optimizer." To me, it sounds like there is no risk of
going over the max optimizer input voltage. I would want to verify this
with SolarEdge prior to designing any systems, but it seems like a good
idea to explore!

I was recently on another group chat, and someone mentioned being in a
similar predicament to you. They want to upgrade an old central inverter.
Anyway, they had found that the SMA CORE1 33 kW unit at least can be strung
up to work with 600 VDC modules and wiring:
https://files.sma.de/downloads/STPCORE1-DS-en-28.pdf?_ga=2.30799225.717469396.1631144387-1894865662.1631144383
I'm sure you'd have to redo a lot of the conduit and wire to accommodate
several smaller inverters, but this might be worth exploring as well.

August
Luminalt


On Wed, Sep 8, 2021 at 4:13 PM William Miller <william at millersolar.com>
wrote:

> Friends:
>
>
>
> I learned a new buzzword recently:  “Re-powering.”  It means replacing
> inverters on an existing PV system of ten or more years old.  Due to the
> high number of systems of this vintage it appears that re-powering has
> become somewhat of a sub-industry.  The big problem is these systems are
> all 600 Volt  limited PV panels, combiners and re-combiners and there are
> no 600 volt utility grade inverters being manufactured.
>
>
>
> I am working on a utility scale system
> <https://millersolar.com/MillerSolar/Portfolio/Commercial/CommercialTracker/CommercialTracker.html>
> built about 14 years ago that fits the description above.  There are two
> 250KVA Xantrex GT250 inverters and one has failed.  The question of the
> moment is:  Repair or replace?
>
>
>
> Repair:  If we fix these inverters, can we count on support in the
> future?    We can negotiate a service contract with Schneider at a cost yet
> to be revealed.  This requires we buy a spare parts kit for about $100K.
> There are a few other companies that claim to offer repair services on
> these inverters but none has followed through.
>
>
>
> Replace:  The PV plant is built with panels and BOS all limited to 600 VDC
> max.  There are no more 600 volt input utility scale inverters being built,
> or at least none that I have found.  If we install a 1000 or 1500 volt
> inverter we may have to replace the entire PV array and BOS.  It may be
> possible to convert the output of the existing panels to a higher voltage
> with DC-DC converters.
>
>
>
> Here are the options I see:
>
>
>
> Optimizers: One purveyor of optimizers is Solar Edge.  Solar Edge offers a
> 100 KVA inverter.  This inverter requires DC input of 850 volts.  The
> inverter requires optimizers to obtain this voltage.  The question:  Do the
> optimizers isolate the PV from the higher string voltages in the case of a
> catastrophic failure of one or more of the optimizers?
>
>
>
> Repower with outboard DC-DC voltage converters, such as provided by
> Alencon Systems.  Solectria has successfully done this.  Here
> <https://alenconsystems.com/learning/pv-retrofits-with-transformerless-inverters/>
> is a paper on the subject.
>
>
>
> If anyone has dealt with this issue before I would sure appreciate any
> wisdom.
>
>
>
> Here is a link
> <https://millersolar.com/MillerSolar/case_studies/30-Re-Powering/re-powering.html>
> to a web-page I built for this project.
>
>
>
> Thanks,
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210908/84fc89d3/attachment.htm>


More information about the RE-Wrenches mailing list