[RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
William Miller
william at millersolar.com
Wed Sep 8 17:45:57 EDT 2021
Friends:
I learned a new buzzword recently: “Re-powering.” It means replacing
inverters on an existing PV system of ten or more years old. Due to the
high number of systems of this vintage it appears that re-powering has
become somewhat of a sub-industry. The big problem is these systems are
all 600 Volt limited PV panels, combiners and re-combiners and there are
no 600 volt utility grade inverters being manufactured.
I am working on a utility scale system
<https://millersolar.com/MillerSolar/Portfolio/Commercial/CommercialTracker/CommercialTracker.html>
built about 14 years ago that fits the description above. There are two
250KVA Xantrex GT250 inverters and one has failed. The question of the
moment is: Repair or replace?
Repair: If we fix these inverters, can we count on support in the future?
We can negotiate a service contract with Schneider at a cost yet to be
revealed. This requires we buy a spare parts kit for about $100K. There
are a few other companies that claim to offer repair services on these
inverters but none has followed through.
Replace: The PV plant is built with panels and BOS all limited to 600 VDC
max. There are no more 600 volt input utility scale inverters being built,
or at least none that I have found. If we install a 1000 or 1500 volt
inverter we may have to replace the entire PV array and BOS. It may be
possible to convert the output of the existing panels to a higher voltage
with DC-DC converters.
Here are the options I see:
Optimizers: One purveyor of optimizers is Solar Edge. Solar Edge offers a
100 KVA inverter. This inverter requires DC input of 850 volts. The
inverter requires optimizers to obtain this voltage. The question: Do the
optimizers isolate the PV from the higher string voltages in the case of a
catastrophic failure of one or more of the optimizers?
Repower with outboard DC-DC voltage converters, such as provided by Alencon
Systems. Solectria has successfully done this. Here
<https://alenconsystems.com/learning/pv-retrofits-with-transformerless-inverters/>
is a paper on the subject.
If anyone has dealt with this issue before I would sure appreciate any
wisdom.
Here is a link
<https://millersolar.com/MillerSolar/case_studies/30-Re-Powering/re-powering.html>
to a web-page I built for this project.
Thanks,
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210908/39061ea5/attachment.htm>
More information about the RE-Wrenches
mailing list