[RE-wrenches] Over-torquing Module Clamps?
Corey Shalanski
coresolar at gmail.com
Wed Sep 8 00:41:49 EDT 2021
Hi Will,
I'm not sure if this is what you were asking (I see that your message was
directed to Jerry), but we 'discovered' the over torquing by setting our
torque wrench on the spec value and confirming that the wrench 'clicked,'
and then progressively increased the setting higher and continued checking
until the wrench did not click and nudged the nut a bit.
--
Corey
On Tue, Sep 7, 2021 at 7:29 AM Will White <will at solarenergy.org> wrote:
> Jerry,
>
> I'm curious, how did they prove over torquing? When doing inspections it's
> easy to find connectors that are under torqued but I haven't heard of a
> reliable way to check for over torque.
>
> Thanks,
> Will
>