If the inside of a 3R enclosure isn't considered dry enough for a buchanan
crimp/cap, then there's millions of 3R panels with breakers and busbars in
them that would have the same problem.

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Mon, Aug 16, 2021 at 12:03 PM Isaac Opalinsky <
David.Opalinsky at sunpower.com> wrote:

> Adam,
>
>
>
> I assume it’s a NYSERDA inspector that’s pushing back, correct? We’ve
> dealt with this issue a number of times, and while I will argue until I’m
> blue in the face that the code does not consider the inside of a properly
> installed NEMA 3R enclosure a damp/wet location, NYSERDA has not accepted
> that argument.
>
>
>
> To be clear, the Buchanan splice caps and insulators are only rated for
> dry locations.
>
>
>
> I’ve heard that NYSERDA has allowed them to be used with dielectric gel
> applied to the interior of a splice cap insulator, but have not been able
> to confirm.
>
>
>
> Best Regards,
>
> *Isaac Opalinsky* | Director, Applications & Technical Support
>
> mobile 443-277-6286 | isaac.opalinsky at sunpower.com
>
> [image: sp_2014_logo_black_orange_CMYK-01]
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *AE Solar
> *Sent:* Monday, August 16, 2021 2:55 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* [EXT] [RE-wrenches] Buchanan Crimps in Outdoor Boxes
>
>
>
> *External Email - *Use caution when responding, clicking, and/or
> downloading attachments.
> ------------------------------
>
> Wrenchers,
>
> Some point back we transitioned from polaris lugs to buchanan crimps/caps
> (doping our wires in noalox) for our jbox splices. I know there have been a
> few conversations on here about this. Seems like a much more robust
> connection than anything we have used prior. But now we have an inspector
> who isn't in support of using them for outdoor/damp locations. To be fair
> (although it seems like a far superior connection) Ideal doesn't have
> documentation to support outdoor use. I know a lot of folks on here have
> had solid/long lasting results though. In any event, we may have to
> transition away from buchanan crimps and wondering what you all recommend
> as your second (or first) choice? Or if anyone has experience with
> supporting this application when dealing with inspectors? Do we go back to
> polaris lugs? I know there was a conversation a while back about failures
> with those...
>
> Thanks for any thoughts.
>
> Adam
>
>
>
> Adam Katzman
> Autonomous Energies
> PO Box 1245
>
> Kingston, NY 12402
> www.autonomousenergies.com
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.autonomousenergies.com&d=DwMFaQ&c=Kv2S0ZicsIm17HTFqYG_Og&r=RD0lHHgQqAl7xvyDm5AiPkLCedjBloPiZPB0MsAPMCE&m=_mjHpHDfeE0DA7KJAxQp-6Q_uNnHsFLwm52PqJ_Zugw&s=TvRw39ewcR48vbSFcdNGGl_zKXV7wLvhwtjdxDX2v_w&e=>
> (518) 567-1468
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210816/a1ed0556/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 5843 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210816/a1ed0556/attachment.png>


More information about the RE-Wrenches mailing list