[RE-wrenches] High to normal SG
Steve Higgins
steve at surrette.com
Wed Jul 21 10:44:31 EDT 2021
FLA batteries cells fail generally in two manners.
Open Cell and Shorted.
Open Cells are more resistive and "Eat up" charging voltage which denies
voltage and charging potential to the rest of the bank so the entire bank
sags. This is the most common type of failure.
Shorted Cells are less resistive so they allow voltage and current to pass
on to the rest of the cells in the string. This causes an overcharge
condition because the dead cell isn't dropping any voltage and the rest of
the cells in the string become "overcharged".
Sometimes SG's will look good, but when the bank is under load you will see
the voltage drop off quickly. This is often the shorted cell.
Battery SG's are like Goldilocks and the three bears.. There is too
high... Too low and Just right... Too low and you lose capacity and this
causes sulfation, which will cause overheating, excessive water use, and
will lead to failure. This is the most common way an FLA battery bank
dies is low SG's are not corrected soon enough and the bank sulfates.
Too high, and you'll get great capacity, for a while, but that higher
acidity will cause corrosion on the plates which will act a lot like
sulfation. On these, you will often see a darker electrolyte as the
higher acidity/corrosion is eating away at the active material of the
plates.
To figure this out what you need to do is...
1. Charge the bank to what you think is full or close to it..
2. Find the 10 Hour Discharge Rate of the bank. (C/10 Discharge Current)
3 Apply load as close as you can get it by running loads in the house.
You will be running this test for 2-5 hours depending on test results.
4. Monitor battery voltages during this test every 30-60 mins.
individual battery voltages should stay pretty close to each other as they
discharge, If you start to see one or two batteries sag in voltage before
the rest you have weak or dying cells.
My bet is you have 1 or two cells that have failed and this is the reason
for the LBCO...
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020 m +1.206.790.5840
f +1.902.597.8447 e steve at surrette.com
<#SignatureSanitizer_SafeHtmlFilter_> <http://www.facebook.com/RollsBattery>
<http://www.facebook.com/RollsBattery> <http://www.twitter.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------
On Wed, Jul 21, 2021 at 7:24 AM Jay <jay.peltz at gmail.com> wrote:
> And what color is the electrolyte?
>
> On Jul 21, 2021, at 8:02 AM, Jay <jay.peltz at gmail.com> wrote:
>
>
> Hi Jeremy
>
> I would like to know brand and model of battery first.
>
> Jay
> Peltz power
>
> On Jul 21, 2021, at 7:22 AM, Jeremy Rodriguez <allsolarjeremy at msn.com>
> wrote:
>
> What’s going on with a battery bank that reads 1.275 SG on all the
> batteries but one, which has cell readings slightly higher.
> The bank is probably 7 years old and this is not a full time residence.
> It’s shutting down with LBCO error.
> I need to go check the site, but I’d expect a dead or weak cell here.
> What else can be checked , battery wise?
>
>
>
> Jeremy Rodriguez
> Solar Installation / Design Expert
> All Solar, Inc.
> 1453 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210721/43c5d47a/attachment.htm>
More information about the RE-Wrenches
mailing list