[RE-wrenches] Is Solark UL 9540 Certified?
Lorenzo Ortiz
lorenzo at cal-solar.com
Tue Jul 20 15:17:12 EDT 2021
Yessir, good old California...
On Tue, Jul 20, 2021 at 11:05 AM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:
> Sounds like California Loren?
>
> I use Schneider and they have UL9540 certs.
>
> Here is a link to them and yes I have been asked this locally.
>
>
> https://solar.schneider-electric.com/schneider-electric-solar-and-discover-battery-attain-ul-9540-certification-for-xw-pro-and-aes-batteries/
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
> On Tue, 20 Jul 2021 10:22:43 -0700, Lorenzo Ortiz <lorenzo at cal-solar.com>
> wrote:
>
> Wrenches,
>
> We have recently had an AHJ reject our Solark 12k system with Simpliphi
> batteries stating:
> *"Energy storage systems are required to be listed per UL 9540 per NEC
> 706.5 (See also Annex A in the NEC, under energy storage systems). The
> Sol-Ark system is not listed and tested per UL 9540 but is only listed per
> UL 1741. The complete system (ie. batteries, inverter, and any other
> components associated with the energy storage system) must be listed per UL
> 9540. Please provide documentation and certification sheets (from a
> Nationally Recognized Testing Lab (NRTL)) for both the batteries and SolArk
> inverter to show that all components are tested and certified per UL 9540.
> If it cannot be shown that the batteries are tested and listed with SolArk
> inverters per UL 9540, then such system cannot be installed and a different
> system that is listed and tested per UL 9540 must be chosen for the
> project.*
>
> Have any of you run into this with Solark? Is the plans-checker in the
> wrong about the entire system needing to meet the standard and not just the
> batteries? The code language is kind of confusing. I can't find any
> documentation on Solark's website regarding UL 9540. I know Tesla and
> Simpliphi have recently put out documentation regarding this.
>
> Thanks in advance for your help.
>
> --
> [image: California Solar Electric Cooperative]
> <https://californiasolarco.com/>
>
>
> Loren Ortiz - Technical Design Specialist
>
> Board Member & Worker Owner
>
> loren at cal-solar.com | www.cal-solar.coop
>
> Office: (530) 274-3671
>
> Fax: (530) 477-7571 CSLB #779624
>
> Showroom: 149 E Main St. Grass Valley, CA 95945
> [image: NABCEP] <https://www.nabcep.org/>
>
>
>
>
>
>
> <https://californiasolarco.com/quote/>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
[image: California Solar Electric Cooperative]
<https://californiasolarco.com/>
Loren Ortiz - Technical Design Specialist
Board Member & Worker Owner
loren at cal-solar.com | www.cal-solar.coop
Office: (530) 274-3671
Fax: (530) 477-7571 CSLB #779624
Showroom: 149 E Main St. Grass Valley, CA 95945
[image: NABCEP] <https://www.nabcep.org/>
--
<https://californiasolarco.com/quote/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210720/e90990ae/attachment.htm>
More information about the RE-Wrenches
mailing list