We have recently had an AHJ reject our Solark 12k system with Simpliphi
batteries stating:
*"Energy storage systems are required to be listed per UL 9540 per NEC
706.5 (See also Annex A in the NEC, under energy storage systems). The
Sol-Ark system is not listed and tested per UL 9540 but is only listed per
UL 1741. The complete system (ie. batteries, inverter, and any other
components associated with the energy storage system) must be listed per UL
9540. Please provide documentation and certification sheets (from a
Nationally Recognized Testing Lab (NRTL)) for both the batteries and SolArk
inverter to show that all components are tested and certified per UL 9540.
If it cannot be shown that the batteries are tested and listed with SolArk
inverters per UL 9540, then such system cannot be installed and a different
system that is listed and tested per UL 9540 must be chosen for the
project.*
Have any of you run into this with Solark? Is the plans-checker in the
wrong about the entire system needing to meet the standard and not just the
batteries? The code language is kind of confusing. I can't find any
documentation on Solark's website regarding UL 9540. I know Tesla and
Simpliphi have recently put out documentation regarding this.
Thanks in advance for your help.
--
[image: California Solar Electric Cooperative]
<https://californiasolarco.com/>
Loren Ortiz - Technical Design Specialist
Board Member & Worker Owner
loren at cal-solar.com | www.cal-solar.coop
Office: (530) 274-3671
Fax: (530) 477-7571 CSLB #779624
Showroom: 149 E Main St. Grass Valley, CA 95945
[image: NABCEP] <https://www.nabcep.org/>
--
<https://californiasolarco.com/quote/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210720/f76abd22/attachment.htm>
More information about the RE-Wrenches
mailing list