[RE-wrenches] outback grid tie help

Darryl Thayer darylsolar1 at gmail.com
Mon Jul 19 22:00:48 EDT 2021


Hi Jay, here are my guesses:
1) Customer is using all the power (3.5 is not a large array)
2)  Per William Miller, the batteries are shot.
3) combination of 1 &2
4) Bulk voltage is too high, daily trying to go to bulk voltage drives the
batteries to the grave.  Float voltage is too high, acting as a low charge,
holding off sell.  The return amps never drop to an acceptable level.
5) What is the sell voltage?  Is it too high?
I feel insecure in telling you my settings as I look to you as one of the
top people in the field.

On Mon, Jul 19, 2021 at 6:25 PM Jay <jay.peltz at gmail.com> wrote:

> I’ve had someone from application engineering at Outback check the
> settings.
>
> All appear normal and correct.
>
> I’m going to be checking the deep setting on grid sell which is most
> likely the culprit.
>
> Thanks for all the advice and I’ll let you all know what find.
>
> Jay
>
> On Jul 19, 2021, at 4:11 PM, Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
> 
> Jay
> In Optics RE
> Mate 3S verify that the firmware is 1.4.6
> under global charge are all switches "disabled"
> in the GS AC Input "Grid",
> Charger "Off",
> "Grid Tie" set
> Offset enable "Yes"
> sell is up to you and battery manufacture
> Jerry
>
> On Sun, Jul 18, 2021 at 1:44 PM jay <jay.peltz at gmail.com> wrote:
>
>> HI All,
>>
>> I”m trying to diagnose the following system I didn’t install.
>>
>> 4 year old system grid tie battery back up.
>>
>> Radian 4048
>> flexmax 80
>> 3500 watts PV
>> fndc
>> it is on opticsRE
>>
>> The symptoms are that its not selling much at all.  Mostly when it is
>> about 1kw max PV production and .8kw selling.  I have disconnected the FNDC
>> and after that it did seem to work better.
>>
>> Usually it will sell a bit, then buy a bit then sell and so on.  Grid
>> voltage is very constant at around 246vac.
>>
>> I’ve been through the settings a few times with tech support, made
>> adjustments and for a while it was selling pretty normally, but again today
>> 0 production, CC is at float.
>>
>> I have not been to the site, I was just trying to do this all by optics.
>> But I’m going to have to go.   I think there are 3 possible issues.
>>
>> 1. the customer has always thought the production is low.  And from what
>> I’ve seen that is true.  This is in a very sunny place, no shade so with
>> 3.5kw, 1kw is very low which I think they may have  a few strings of the
>> array are not connected. However why that bothers me is that the VOC/VMP
>> voltages are too close in looking at the CC.  Which leads me to think its
>> been told to back off to the 1.0kw, by some setting, see #2. And its always
>> around .8 selling and around 1kw output from the array.
>>
>> 2.  There is a programing issue.
>>
>> 3. There is a hardware issue.
>>
>>
>> If someone wants to look at the site, I have the info and they can log
>> in.
>> Or if they want to provide settings for me to triple check, that would be
>> great
>> and
>> if they have any ideas as to why its acting like it is, very much
>> appreciated
>> So far even though tech support has viewed in on Optics and have had some
>> recommendations as to settings, its not fixed the issue.
>>
>> thanks in advance,
>>
>> jay
>>
>> peltz power
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210719/d33f1769/attachment.htm>


More information about the RE-Wrenches mailing list