[RE-wrenches] How Best to Load Test 2 V Cells
Jeff Clearwater
jeffc at villagepowerdesign.com
Wed Jul 14 17:43:20 EDT 2021
Yes good thought Chris -I doubt if there is an IR tester anywhere on the
island - but when I go I will for sure look at that - thanks for that.
How would one measure battery resistance with voltage present? I guess
with a known voltage applied and current held constant one could
calculate? but then how do you know you are measuring resistance vs
storing energy? I don't think that's possible - others?
jc
> Chris Worcester <mailto:chris at solarwindworks.com>
> July 14, 2021 at 2:14 PM
> Has an infra-red thermometer been used on every battery's terminals to
> check for resistance? I recall, although this might be my own
> thoughts, that internal resistance of each cell can be measured with
> an ohm meter...
>
>
>
> Chris Worcester
> chris at solarwindworks.com
> 530-448-9692
>
> Sent from my Samsung Galaxy s9.
>
>
> -------- Original message --------
> From: Jeff Clearwater <jeffc at villagepowerdesign.com>
> Date: 7/14/21 1:42 PM (GMT-08:00)
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] How Best to Load Test 2 V Cells
>
> Hey Jay,
>
> Yes the Sunny island Master of this Quad SI AC-coupled off-grid system
> has been giving automatic Eq and Full charge charges perodically as
> appropriate to this 48 V EnergyCell RE2700 pack.
>
> We are getting whole pack volt drops way before we should at 600 well-
> maintained cycles. When we do whole pack testing - when the voltage
> drops off there are 5 of the 24 cells lagging - their voltage drops
> faster than the rest - but they operate well between 50%-100% - all
> busbars have been triple checked for corrosion and tourque.
>
> So it looks like they just aged prematurely - so I'm in the process of
> collating data from EnnexOS to get exact numbers on how they've been
> treated. But even with a few hard cycles they should held up better
> than they have. So perhaps a warranty claim - I've gone through
> charge settings with SMA etc. I did have the AHrs programmed slightly
> below rated AHrs due to confusion of whether the SI uses the 20 hr or
> 10 hr rate (in Europe they use 10 but apparently - unbeknowst to me -
> the US SI uses the 20 Hr - I swear SMA tech support years ago told me
> 10 hours) but now they are claiming that might be the culprit - I
> have a hard time believing that setting the Ahour rating in the SI to
> 2100 instead of 2288 as rated would lead to pack failure - but they
> are claiming that could have contributed.
>
> Thoughts?
>
> Best,
>
> Jeff
>
>
>
>
> Jeff Clearwater <mailto:jeffc at villagepowerdesign.com>
> July 14, 2021 at 1:42 PM
> Hey Jay,
>
> Yes the Sunny island Master of this Quad SI AC-coupled off-grid system
> has been giving automatic Eq and Full charge charges perodically as
> appropriate to this 48 V EnergyCell RE2700 pack.
>
> We are getting whole pack volt drops way before we should at 600 well-
> maintained cycles. When we do whole pack testing - when the voltage
> drops off there are 5 of the 24 cells lagging - their voltage drops
> faster than the rest - but they operate well between 50%-100% - all
> busbars have been triple checked for corrosion and tourque.
>
> So it looks like they just aged prematurely - so I'm in the process of
> collating data from EnnexOS to get exact numbers on how they've been
> treated. But even with a few hard cycles they should held up better
> than they have. So perhaps a warranty claim - I've gone through
> charge settings with SMA etc. I did have the AHrs programmed slightly
> below rated AHrs due to confusion of whether the SI uses the 20 hr or
> 10 hr rate (in Europe they use 10 but apparently - unbeknowst to me -
> the US SI uses the 20 Hr - I swear SMA tech support years ago told me
> 10 hours) but now they are claiming that might be the culprit - I
> have a hard time believing that setting the Ahour rating in the SI to
> 2100 instead of 2288 as rated would lead to pack failure - but they
> are claiming that could have contributed.
>
> Thoughts?
>
> Best,
>
> Jeff
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210714/3414e440/attachment.htm>
More information about the RE-Wrenches
mailing list