[RE-wrenches] How Best to Load Test 2 V Cells

Dave Angelini Offgrid Solar offgridsolar at sti.net
Wed Jul 14 17:41:42 EDT 2021



Not sure about SMA but XW and Radian would definatley change the absorb
time. Having the lower AH number would be a longer absorb time on an XW.
That would be a good thing as it would get the full programmed absorb
instead of 2% of the programmed AH. It is a whichever comes first
algorithm.  

Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060

On Wed, 14 Jul 2021 13:42:23 -0700, Jeff Clearwater 
wrote:  Hey Jay,

 Yes the Sunny island Master of this Quad SI AC-coupled
off-grid system has been giving automatic Eq and Full charge charges
perodically as appropriate to this 48 V EnergyCell RE2700 pack.

 We are
getting whole pack volt drops way before we should at 600 well- maintained
cycles. When we do whole pack testing - when the voltage drops off there
are 5 of the 24 cells lagging - their voltage drops faster than the rest -
but they operate well between 50%-100% - all busbars have been triple
checked for corrosion and tourque. 

 So it looks like they just aged
prematurely - so I'm in the process of collating data from EnnexOS to get
exact numbers on how they've been treated. But even with a few hard cycles
they should held up better than they have. So perhaps a warranty claim -
I've gone through charge settings with SMA etc. I did have the AHrs
programmed slightly below rated AHrs due to confusion of whether the SI
uses the 20 hr or 10 hr rate (in Europe they use 10 but apparently -
unbeknowst to me - the US SI uses the 20 Hr - I swear SMA tech support
years ago told me 10 hours) but now they are claiming that might be the
culprit - I have a hard time believing that setting the Ahour rating in the
SI to 2100 instead of 2288 as rated would lead to pack failure - but they
are claiming that could have contributed.

 Thoughts?

 Best,

 Jeff

   
Jay [3] July 14, 2021 at 1:15 PM    Hi Jeff   If it's the energy cell xlc
from Outback then it shows an eq requirement.    If not that battery, most
industrial quality VRLA I've seen have a eq requirement, conditioning
charge or something similar.  And the lowering of capacity is common from
experience.    Question What equipment/brand is charging it?   Jay   Peltz
power      Jeff Clearwater [4] July 14, 2021 at 11:32 AM    Thanks Dave -
yes I've done whole pack load testing. The deal with this pack though is
that it is so remote and the expense of "just replace the pack" in terms of
shipping and labor is extreme - (tiny Bahaman island with only regular
small boat access}

 And if it was toward the end of the pack's life anyway
I'd not mess around - but with only 600 well documented cylces on a $25K
pack - and with probably half that again in shipping and labor to replace -
I'm needing to carefully document the lagging cells for either a warranty
claim or at least to make good decisions going forward.

 It's easy to
access the cells as this is an EnergyCell AGM stack with easily accessible
terminals and removable terminal bars.

 If we replace we'd go LFP - on the
order of 100 KWHrs. So no small decision for the customer - so worth the
testing.

 Thanks!

 Jeff Clearwater
 Village Power Design

www.villagepowerdesign.com [5]


_______________________________________________
List sponsored by Redwood
Alliance

Pay optional member dues here: http://re-wrenches.org [6]

List
Address: RE-wrenches at lists.re-wrenches.org [7]

Change listserver email
address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[8]

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[9]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[10]

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
[11]

Check out or update participant
bios:
http://www.members.re-wrenches.org [12]

   

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridsolar at sti.net
[3]
mailto:jay.peltz at gmail.com
[4] mailto:jeffc at villagepowerdesign.com
[5]
http://www.villagepowerdesign.com
[6] http://re-wrenches.org
[7]
mailto:RE-wrenches at lists.re-wrenches.org
[8]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[9]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[10]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[11]
http://www.re-wrenches.org/etiquette.htm
[12]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210714/5b8de190/attachment.htm>


More information about the RE-Wrenches mailing list