[RE-wrenches] How Best to Load Test 2 V Cells
Jeff Clearwater
jeffc at villagepowerdesign.com
Wed Jul 14 16:42:23 EDT 2021
Hey Jay,
Yes the Sunny island Master of this Quad SI AC-coupled off-grid system
has been giving automatic Eq and Full charge charges perodically as
appropriate to this 48 V EnergyCell RE2700 pack.
We are getting whole pack volt drops way before we should at 600 well-
maintained cycles. When we do whole pack testing - when the voltage
drops off there are 5 of the 24 cells lagging - their voltage drops
faster than the rest - but they operate well between 50%-100% - all
busbars have been triple checked for corrosion and tourque.
So it looks like they just aged prematurely - so I'm in the process of
collating data from EnnexOS to get exact numbers on how they've been
treated. But even with a few hard cycles they should held up better
than they have. So perhaps a warranty claim - I've gone through charge
settings with SMA etc. I did have the AHrs programmed slightly below
rated AHrs due to confusion of whether the SI uses the 20 hr or 10 hr
rate (in Europe they use 10 but apparently - unbeknowst to me - the US
SI uses the 20 Hr - I swear SMA tech support years ago told me 10
hours) but now they are claiming that might be the culprit - I have a
hard time believing that setting the Ahour rating in the SI to 2100
instead of 2288 as rated would lead to pack failure - but they are
claiming that could have contributed.
Thoughts?
Best,
Jeff
> Jay <mailto:jay.peltz at gmail.com>
> July 14, 2021 at 1:15 PM
> Hi Jeff
>
> If it’s the energy cell xlc from Outback then it shows an eq requirement.
>
> If not that battery, most industrial quality VRLA I’ve seen have a eq
> requirement, conditioning charge or something similar.
> And the lowering of capacity is common from experience.
>
> Question
> What equipment/brand is charging it?
>
> Jay
>
> Peltz power
>
> Jeff Clearwater <mailto:jeffc at villagepowerdesign.com>
> July 14, 2021 at 11:32 AM
> Thanks Dave - yes I've done whole pack load testing. The deal with
> this pack though is that it is so remote and the expense of "just
> replace the pack" in terms of shipping and labor is extreme - (tiny
> Bahaman island with only regular small boat access}
>
> And if it was toward the end of the pack's life anyway I'd not mess
> around - but with only 600 well documented cylces on a $25K pack - and
> with probably half that again in shipping and labor to replace - I'm
> needing to carefully document the lagging cells for either a warranty
> claim or at least to make good decisions going forward.
>
> It's easy to access the cells as this is an EnergyCell AGM stack with
> easily accessible terminals and removable terminal bars.
>
> If we replace we'd go LFP - on the order of 100 KWHrs. So no small
> decision for the customer - so worth the testing.
>
> Thanks!
>
> Jeff Clearwater
> Village Power Design
> www.villagepowerdesign.com <http://www.villagepowerdesign.com>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210714/95439143/attachment.htm>
More information about the RE-Wrenches
mailing list