[RE-wrenches] Grounding Top of Pole Mount Array with a Ufer
frenergy
frenergy at psln.com
Thu Jun 24 18:49:04 EDT 2021
Ray,
I couldn't agree more, its been my experience over the
years that using 20 feet of #4 rebar in a building's footing was kosher
and accepted NEC 250.52(3). There's a heck of a lot more surface area
in 8" pipe 5-6 feet into the earth than rebar in a foundation footing.
The ground at the bottom of the pole footing is also more likely to be
damper. Our AHJ has always accepted the steel pole as a ground
rod....common sense prevails sometimes.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
On 6/24/2021 7:31 AM, Ray wrote:
> Usually a steel pole in concrete has enough surface area to qualify as
> a plate electrode under 250.52(A)(7). It needs to be at least 2 sq ft
> and 1/4" thick, and have an electrically conductive surface. So we
> just drill and tap our ground connection into the pole, near the
> combiner box.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 6/24/21 8:16 AM, Dana Orzel wrote:
>> For all of our free standing arrays we now use a Ufer clamp to the
>> rebar either cage or just anti spin rebar that is welded to the pole
>> in the concrete, with #4 braided copper up to the pole combiner box,
>> inverter, etc. for our ground.
>> With a pole mount & a concrete base it is way easier & less expensive
>> than a ground rod, & the inspector seems happier with this approach.
>>
>>
>>
>> Dana Orzel Great Solar Works, Inc.
>> C - 208.721.7003 dana at solarwork.com
>> Idaho Contractor - # 028765 Idaho PV # 028374
>> NABCEP # 051112-136 www.greatsolarworks.com
>> "Responsible Technologies for Responsible People since 1988"
>> Please consider the environment before printing this email.
>>
>>
>> -----Original Message-----
>> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On
>> Behalf Of palumbo131m at gmail.com
>> Sent: Wednesday, June 23, 2021 9:33 PM
>> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> Subject: Re: [RE-wrenches] Top of Pole Mount Array on Ledge
>>
>> Ben,
>> There is a way if the ledge is solid and true. Twice I have done the
>> following with ledge at 18” to 24” below grade. Excavate down to
>> ledge, drill down into the ledge and you will determine the
>> suitability of the following method. Drill for a pattern of many
>> rebar penetrations in to the ledge. Drill to a reasonable depth (as
>> deep into the ledge as you are able) in my case it was based on our
>> drilling tool and bit length capabilities. We used a large sono tube.
>> 42” as a recall, both of these jobs were over 12 years ago and my
>> recall on the exact size may be off.
>> Determine the best adhesive product to use in your drilled holes for
>> the rebar, again my memory fails as to what we used based on
>> recommendation from a local civil engineer. The sono tube height
>> above grade was determined to be 2’ for one TPM12 and 3.5’ above
>> grade for a TPM16. Depth down to the ledge determines how high above
>> grade you need the concrete footing/base. Use rebar lengths that will
>> end a few inches below the finished surface. For grounding you can
>> coil up ground wire and lay it on the surface of the ledge before
>> your concrete pour. I ran the ground wire through a short length of
>> 1/2” or 3/4” PVC conduit, to protect the copper ground wire where it
>> comes out of the concrete. Place the conduit coming out of the
>> concrete with the ground wire just to the side of where the mounting
>> plate base for the TPM will be and fill the PVC conduit with a good
>> caulk sealer to keep air and water out of this hole as a nexus of
>> concrete, and air will corrode the copper. The TPM’s for those two
>> jobs were made of 8” SCHD 80 steel, we had a large plate welded to
>> the bottom with 4 vertical side supports on the pipe up about a foot.
>> Place the appropriate sized anchor bolts in the concrete pour to
>> match your TPM base. Both of these TPM’s have worked out well over
>> the years. Local conditions will determine the suitability of this
>> method.
>>
>>
>> Sent from my iPhone
--