[RE-wrenches] Sol-Ark 12k w/ Generac Transfer Switch

Chris Mason cometenergysystems at gmail.com
Fri Jun 18 11:21:11 EDT 2021


I think you are confusing the transfer switch that can me controlled by the
PWRcell inverter.
All Guardians can be started by two wire control. It does not violate your
warranty. When you start using relays in the transfer switch, that
invalidates your warranty.

On Fri, Jun 18, 2021 at 10:16 AM <drake.chamberlin at redwoodalliance.org>
wrote:

> I've controlled Generac Guardians, using the transfer switch and adding
> relays so the inverter decides when it should start. These were out of
> warranty units. Checking with Generac about a proposed new generator, I was
> told that it would void the warranty to do that. I was told that a new
> Generac is supposed to come our around the end of the year that can be
> controlled by an inverter.
>
> Drake
>
>
>
> Drake Chamberlin
>
> Athens Electric LLC
>
> Ohio Electrical Contractor’s License 44810
>
> CO Master Electrician’s License 4526
>
> NABCEP Certified PV Installation Professional
>
> athens-electric.com
>
>
> ---
>
>
>
> On 2021-06-17 09:41, rick at solshineenergy.com wrote:
>
> Wrenches,
>
> I'm looking to tie in a Generac Powerpact 7.5kW generator with transfer
> switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC)
> capability, however, the Generac transfer switch operates on loss of 240V.
> Is my only option to use a relay driven by the two wire start to drop 240V
> to the transfer switch?
>
> Thank you,
>
> rick brown
> SolShine Energy Alternatives, LLC
> Electrical & Solar Contracting Services
> www.SolShineEnergy.com
> Check, Virginia 24072
> Office: 540.235.3095
> Mobile: 540.808.9502
>
> VA Class A Contractor Lic# 2705147660
> VA Master Electrician Lic# 2710062762
> VA Alternative Energy Systems Installer
> NABCEP Certified PV Installation Professional 110112-21
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210618/a85dc152/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: PastedGraphic-1.tiff
Type: image/tiff
Size: 15860 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210618/a85dc152/attachment.tiff>


More information about the RE-Wrenches mailing list