[RE-wrenches] Sol-Ark 12k w/ Generac Transfer Switch

Chris Mason cometenergysystems at gmail.com
Thu Jun 17 15:58:34 EDT 2021


And just like that, I found the instructions for two wire start of a
Powerpact generator.
https://rexel-cdn.com/Products/Generac/7109.pdf?i=3DE90BD8-3F92-4C63-A833-FEDC1C27B8F7




On Thu, Jun 17, 2021 at 9:41 AM rick at solshineenergy.com <
rick at solshineenergy.com> wrote:

> Wrenches,
>
> I’m looking to tie in a Generac Powerpact 7.5kW generator with transfer
> switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC)
> capability, however, the Generac transfer switch operates on loss of 240V.
> Is my only option to use a relay driven by the two wire start to drop 240V
> to the transfer switch?
>
> Thank you,
>
> rick brown
> SolShine Energy Alternatives, LLC
> Electrical & Solar Contracting Services
> www.SolShineEnergy.com
> Check, Virginia 24072
> Office: 540.235.3095
> Mobile: 540.808.9502
>
> VA Class A Contractor Lic# 2705147660
> VA Master Electrician Lic# 2710062762
> VA Alternative Energy Systems Installer
> NABCEP Certified PV Installation Professional 110112-21
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210617/34efdfe6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: PastedGraphic-1.tiff
Type: image/tiff
Size: 15860 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210617/34efdfe6/attachment.tiff>


More information about the RE-Wrenches mailing list