[RE-wrenches] Sol-Ark 12k w/ Generac Transfer Switch
William Miller
william at millersolar.com
Thu Jun 17 12:11:30 EDT 2021
Friends:
I dislike jury-rigging a generator loss-of-grid start signal to a two-wire start. If the inverters need to be shut down for service or happen to shut down on their own, the generator will start. Not a good design.
William Miller
www.millersolar.com
> On Jun 17, 2021, at 6:48 AM, Dave Tedeyan <dave at sungineersolar.com> wrote:
>
>
> Hi Rick,
> I have a similar situation with a GE transfer switch, but am curious to hear what others have to say. My assumption was that the switch transfers based on loss of 240V from the grid. But I believe (at least with the GE generator) that the transfer switch sends a two wire start signal to the inverter when the transfer switch loses the 240V signal. My plan was to rewire that start signal to the Sol-Ark inverter, but keep the transfer switch as the main service point to prevent any kind of backfeeding to the grid.
> Cheers,
> Dave
>
>> On Thu, Jun 17, 2021 at 9:41 AM rick at solshineenergy.com <rick at solshineenergy.com> wrote:
>> Wrenches,
>>
>> I’m looking to tie in a Generac Powerpact 7.5kW generator with transfer switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC) capability, however, the Generac transfer switch operates on loss of 240V. Is my only option to use a relay driven by the two wire start to drop 240V to the transfer switch?
>>
>> Thank you,
>>
>> rick brown
>> SolShine Energy Alternatives, LLC
>> Electrical & Solar Contracting Services
>> www.SolShineEnergy.com
>> Check, Virginia 24072
>> Office: 540.235.3095
>> Mobile: 540.808.9502
>>
>> VA Class A Contractor Lic# 2705147660
>> VA Master Electrician Lic# 2710062762
>> VA Alternative Energy Systems Installer
>> NABCEP Certified PV Installation Professional 110112-21
>>
>> <PastedGraphic-1.tiff>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
>
> --
> Dave Tedeyan, PE
>
> 1653 Slaterville Road, Ithaca, NY 14850
> Cell: 607-288-2898
> www.sungineersolar.com
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210617/c749dcaa/attachment.htm>
More information about the RE-Wrenches
mailing list