[RE-wrenches] Sol-Ark 12k w/ Generac Transfer Switch

Mac Lewis maclewis1 at gmail.com
Thu Jun 17 11:35:06 EDT 2021


Yes, you need to have a transfer switch with its own brain that doesn't
need the generator controller to decide which source to latch to.

A good example of this is the Kohler line of transfer switches:

The RXT line of transfer switches needs the RDC2 controller (in the
generator) to actually switch to the secondary source and back (this can be
hacked of course).
The RDT line of switches can be independent and work well for these
applications.

Most transfer switches will switch to the neutral position upon loss of
utility but need an energized secondary source to latch into the secondary
position.

You do pay more for the transfer switches with the independent brain but
it's worth not needing to provide added control signalling.



On Thu, Jun 17, 2021 at 9:06 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:

> I have the same question. I assumed an ATS would transfer upon utility
> loss, but I'm learning that some do not transfer until the generator starts
> up. I'm wondering how this works with Sol-Arks given their schematics that
> use ATS in multi-inverter setups for whole home backup (with no generator
> involved).
>
> Jason Szumlanski
>
> On Thu, Jun 17, 2021, 9:48 AM Dave Tedeyan <dave at sungineersolar.com>
> wrote:
>
>> Hi Rick,
>> I have a similar situation with a GE transfer switch, but am curious to
>> hear what others have to say. My assumption was that the switch transfers
>> based on loss of 240V from the grid. But I believe (at least with the GE
>> generator) that the transfer switch sends a two wire start signal to the
>> inverter when the transfer switch loses the 240V signal. My plan was to
>> rewire that start signal to the Sol-Ark inverter, but keep the transfer
>> switch as the main service point to prevent any kind of backfeeding to the
>> grid.
>> Cheers,
>> Dave
>>
>> On Thu, Jun 17, 2021 at 9:41 AM rick at solshineenergy.com <
>> rick at solshineenergy.com> wrote:
>>
>>> Wrenches,
>>>
>>> I’m looking to tie in a Generac Powerpact 7.5kW generator with transfer
>>> switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC)
>>> capability, however, the Generac transfer switch operates on loss of 240V.
>>> Is my only option to use a relay driven by the two wire start to drop 240V
>>> to the transfer switch?
>>>
>>> Thank you,
>>>
>>> rick brown
>>> SolShine Energy Alternatives, LLC
>>> Electrical & Solar Contracting Services
>>> www.SolShineEnergy.com
>>> Check, Virginia 24072
>>> Office: 540.235.3095
>>> Mobile: 540.808.9502
>>>
>>> VA Class A Contractor Lic# 2705147660
>>> VA Master Electrician Lic# 2710062762
>>> VA Alternative Energy Systems Installer
>>> NABCEP Certified PV Installation Professional 110112-21
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
>>
>> --
>> *Dave Tedeyan, PE*
>> [image: Sungineer Solar]
>> 1653 Slaterville Road, Ithaca, NY 14850
>> Cell: 607-288-2898
>> www.sungineersolar.com
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210617/b04aa756/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: PastedGraphic-1.tiff
Type: image/tiff
Size: 15860 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210617/b04aa756/attachment.tiff>


More information about the RE-Wrenches mailing list