Wrenches,
I’m looking to tie in a Generac Powerpact 7.5kW generator with transfer switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC) capability, however, the Generac transfer switch operates on loss of 240V. Is my only option to use a relay driven by the two wire start to drop 240V to the transfer switch?
Thank you,
rick brown