[RE-wrenches] Need some help
Marco Mangelsdorf
marco at pvthawaii.com
Sun Jun 6 12:38:40 EDT 2021
Those dinosaur Trace PV series inverters REQUIRE that isolation transformer
between it and the AC tie-in. As in, it cannot be removed.
So a big question is whether the two inverters are in good working order,
right? I’ve got inverters of that vintage still operating in the field. One
of the common failure modes is the cooling fan failing. Which is an easy
enough repair. By contrast, a board failure is bigger bad news because
I’ve found it impossible to get any replacement parts from Schneider.
marco
On Sunday, June 6, 2021, <pgiroux at mindspring.com> wrote:
> Good morning fellow wrenchers, need some help from those of you that
> have a bit more tenure than I do. Was called to look at a site yesterday
> that is down due to renovations. It is a gas station that has 20 KW worth
> of solar on the canopy, two Trace PV-10208’s and two transformers, one on
> the output of each inverter. The system was shut down during a large
> renovation, wires cut and sort of lost under the pavement during the work.
> We have a good idea where we can dig to locate the conduit for AC but my
> dilemma is the equipment on the canopy. The owner has no idea how old the
> system is and if it was actually working prior to the reno.
>
>
>
> Getting AC back up and running to the canopy may be the easy part, I
> need to understand why there is a transformer along with the Trace inverter
> and how have these inverters held up for 20 + years and based on layout if
> needed can I replace inverter with current tech without rewiring the whole
> canopy ( 264 BP 85 watt panels, wired to combiner box then out to inverters
> ). Power supply at gas station is 208. So, please and thank you in advance,
> any and all help, guidance and ideas greatly appreciated.
>
>
>
> Thank you
>
> Peter Giroux
>
> American Solar & Alternative Energy Solutions inc
>
> Roswell Ga
>
> 678 525 0468
>
-------------- next part --------------