[RE-wrenches] Wago Connectors (221 series)

Jason Szumlanski jason at floridasolardesigngroup.com
Mon May 10 18:20:30 EDT 2021


There is one more thing to consider that just hit me while looking at
a Wago. I don't think the insulation of a #10 PV wire is going to fit into
the 221-6XX connector. I need to check on that.




On Mon, May 10, 2021 at 4:06 PM Chris Schaefer <chris at solarandwindfx.com>
wrote:

> Kudos to Dan Fink. Nice job. Just another reason to send a donation to
> Michael Welch.
>
> Christopher
>
> On Mon, May 10, 2021 at 3:29 PM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>> I agree and I just got written confirmation from Wago that said
>> (regarding the 221-4XX series):
>>
>> WAGO's U.L. Recognition for Series 221 does Not differentiate between AC
>> or DC Just Not to exceed 20A
>>
>> 600V Building Wire or 1000V Luminaires or Signs
>>
>> No Special designation is required.
>>
>> On Mon, May 10, 2021, 2:56 PM Dan Fink <danbob88 at gmail.com> wrote:
>>
>>> Esteemed Wrenches; I spoke with engineers at both Wago and 3M today
>>> regarding the AC vs. DC ratings of Wago 221 and other wire splicing
>>> products. Both engineers stated that standard UL486C (Splicing Wire
>>> Connectors) applies to *both* AC and DC voltages unless the product is
>>> specifically listed for *only *AC or DC.
>>>
>>> They both gave the example that the same applies to the actual wire that
>>> is being spliced: Is the THWN-2 wire we use inside DC OCPD panels
>>> specifically UL rated for DC? *No (UL83)*. Is it acceptable for DC?
>>> *Yes,* we use it all the time for DC circuits. How about USE-2 and MC?
>>> Can we use them for both AC and DC? *Yes, *we use them all the time for
>>> both AC and DC. Is it specifically UL rated for DC? *No. It doesn't
>>> need to be.*
>>>
>>> Of course any wiring device that *disconnects *any circuit under load
>>> must be rated for either AC, DC or both depending on the application. But
>>> wire splicing connectors are not intended as a disconnecting device under
>>> UL486C.
>>>
>>> I hope this clears up any confusion.
>>>
>>> Best regards;
>>>
>>> Dan Fink
>>> Owner, Buckville Energy Consulting LLC
>>> IREC Certified Instructor for PV and Small Wind Installation
>>> NABCEP Certified PV System Inspector
>>> NABCEP PV Associate
>>> d <dan.fink at greendustrialtraining.com>anbob88 at gmail.com
>>> 970-672-4342
>>>
>>>
>>> On Fri, May 7, 2021 at 3:43 PM Jason Szumlanski <
>>> jason at floridasolardesigngroup.com> wrote:
>>>
>>>> In another thread these connectors were discussed recently. There was a
>>>> question regarding the suitability for DC circuits. I don't think we came
>>>> up with any answers or consensus on that. I see the connectors are UL
>>>> listed to the 486C standard. I can't determine whether that is applicable
>>>> to AC and DC circuits. Does anyone know?
>>>>
>>>> I have only used these on AC circuits and they have been very
>>>> effective. Now I'm curious whether they can be used on DC circuits up to
>>>> 600 volts.
>>>>
>>>> While on the subject, I noticed they are UL 467 listed for grounding
>>>> and bonding. That's helpful where you have EGC splices for conductors up to
>>>> #10 AWG inside junction boxes.
>>>>
>>>> Jason Szumlanski
>>>> Florida Solar Design Group
>>>>
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>> <https://mailtrack.io/trace/link/a20495a56b13f233b865955cd966fa29fa89f984?url=http%3A%2F%2Fre-wrenches.org&userId=1613865&signature=c5f7802ba978b116>
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/c74f856037bafbb1bddf21e7183735c523121f7b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4ec7f4b41806af02>
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> <https://mailtrack.io/trace/link/c1a1414a6dbd176ffe8f977df2dbf2dc5cf79aa5?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=8a87b2fb2a113d48>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/9a6e617ca79fce6528e2f788e323746c96d36875?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=05e74901cdfdeaee>
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/bc9d4ccafa1360164db621a72980e8af09cd5f61?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=aa64588409168f73>
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/8417bdcac95161d372264988551c41c12aede2a0?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=365a3f7ad89364fa>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>> <https://mailtrack.io/trace/link/022a660ab8251de0003926a9a9855f6389b3a5a3?url=http%3A%2F%2Fre-wrenches.org&userId=1613865&signature=7deb90ecde643c3b>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/e7343fdf690c2bfeabad10a848d6ac1f69fe2a6a?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5e6ffa103a572d0a>
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://mailtrack.io/trace/link/e645f9cbcc3ac7410ce45a2f67ffb526a2b2d4da?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=eadf7aade0e832b8>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/baab6c6a2fc533c8262daabf7279569a59db4fd5?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5b1a09f9fe6a54ae>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/dd3f697435d2435ed4e037a8389623faf0843d51?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=392c7f86f9bb95ad>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/26dcd4fc901240b72585c7568986187492943deb?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=966e466cebe47689>
>>
>>
>
> --
>
> Chris Schaefer’s
>
> <https://mailtrack.io/trace/link/fd04835003cf70d0c8d524b3f1ef9cbf2dd0e204?url=http%3Awww.solarandwindfx.com&userId=1613865&signature=065d476939d88b28>
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
> <https://mailtrack.io/trace/link/29bcc25fffe437eac59fa6d892bc214744215ada?url=http%3A%2F%2Fwww.solarandwindfx.com&userId=1613865&signature=c7f4dece827c1aea>
> ~ E-mail: chris at solarandwindfx.com <chris at solarandwindfx.com>*
>
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
> <https://mailtrack.io/trace/link/b75e4d46b9ba7048c05e6c96e281676bfe66ce39?url=http%3A%2F%2Fre-wrenches.org&userId=1613865&signature=9694bb29ac394cf7>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/1d06c2fa5f457efb6f96fbffb72808a588cc9edd?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4ffcd841e92a1aa1>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/trace/link/7e403862e13effb5d30134dd3936e24826b61872?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=da0845c3b41ea0a4>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/48bb10268d5f179229496e9ecc583b65d35351bd?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=a91506938cf55880>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/b8ce2678568fa42417073b1b6a3f21413fe3feaf?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f9239b3141fc14a2>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/dc73b972da47708e6a1e00db149054b8786deb8b?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=9b45e369f8c789e0>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210510/45c306a4/attachment.htm>


More information about the RE-Wrenches mailing list