[RE-wrenches] Wago Connectors (221 series)

Ray ray at solarray.com
Mon May 10 15:21:30 EDT 2021


Thanks Dan, that has also been my understanding of all listed 
equipment.  Certain switches etc will say on them "AC only", or give 
different DC ratings.  Otherwise the voltage listing is AC/DC.

Ray Walters
Remote Solar
303 505-8760

On 5/10/21 2:55 PM, Dan Fink wrote:
> Esteemed Wrenches; I spoke with engineers at both Wago and 3M today 
> regarding the AC vs. DC ratings of Wago 221 and other wire splicing 
> products. Both engineers stated that standard UL486C (Splicing Wire 
> Connectors) applies to */both/* AC and DC voltages unless the product 
> is specifically listed for /*only */AC or DC.
>
> They both gave the example that the same applies to the actual wire 
> that is being spliced: Is the THWN-2 wire we use inside DC OCPD panels 
> specifically UL rated for DC? *No (UL83)*. Is it acceptable for DC? 
> *Yes,* we use it all the time for DC circuits. How about USE-2 and MC? 
> Can we use them for both AC and DC? *Yes, *we use them all the time 
> for both AC and DC. Is it specifically UL rated for DC? *No. It 
> doesn't need to be.*
>
> Of course any wiring device that *disconnects *any circuit under load 
> must be rated for either AC, DC or both depending on the application. 
> But wire splicing connectors are not intended as a disconnecting 
> device under UL486C.
>
> I hope this clears up any confusion.
>
> Best regards;
>
> Dan Fink
> Owner, Buckville Energy Consulting LLC
> IREC Certified Instructor for PV and Small Wind Installation
> NABCEP Certified PV System Inspector
> NABCEP PV Associate
> d <mailto:dan.fink at greendustrialtraining.com>anbob88 at gmail.com 
> <mailto:anbob88 at gmail.com>
> 970-672-4342
>
>
> On Fri, May 7, 2021 at 3:43 PM Jason Szumlanski 
> <jason at floridasolardesigngroup.com 
> <mailto:jason at floridasolardesigngroup.com>> wrote:
>
>     In another thread these connectors were discussed recently. There
>     was a question regarding the suitability for DC circuits. I don't
>     think we came up with any answers or consensus on that. I see the
>     connectors are UL listed to the 486C standard. I can't determine
>     whether that is applicable to AC and DC circuits. Does anyone know?
>
>     I have only used these on AC circuits and they have been very
>     effective. Now I'm curious whether they can be used on DC circuits
>     up to 600 volts.
>
>     While on the subject, I noticed they are UL 467 listed for
>     grounding and bonding. That's helpful where you have EGC splices
>     for conductors up to #10 AWG inside junction boxes.
>
>     Jason Szumlanski
>     Florida Solar Design Group
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210510/9464a752/attachment.htm>


More information about the RE-Wrenches mailing list