[RE-wrenches] Wago Connectors (221 series)
William Miller
william at millersolar.com
Fri May 7 20:47:44 EDT 2021
Friends:
Call me old fashioned, but I cannot get any confidence on the Wago
connector. It seems somewhat akin to the back-wire mechanism on a 15A
receptacle. This connection relies on a spring that is subject to
reduction in force when it gets hot. We have seen many of the back-wire
receptacles heat up and get more resistive as heat increases, creating more
heat, etc.
We have learned when connecting battery cables to inverters or batteries
that the best connection does not have any washer or any intermediate
object between one conductor and the other.
I know wire nuts are not ideal (pun intended) but I like my conductors to
be in direct contact, or under a screw terminal where I can determine and
reconfirm the pressure placed on the conductor. It is also necessary to
have control over the pressure applied to the connection, which is why
there are listed torque specs.
Yesterday I was measuring the line voltage on an SB Series 22 inverter.
This unit uses the Wago terminal. There was no way I could get a meter
probe into the Wago to measure line voltage. I had to take the cover off
the electronics sections and measure voltage at the circuit board. I much
prefer a screw terminal I can adjust the torque and get a meter probe onto
it.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Dan Fink
*Sent:* Friday, May 7, 2021 4:01 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Wago Connectors (221 series)
Jason; From the Wago 221 data sheet, it's listed to UL 486C, 600V, 30A, Use
Group C (industrial) . I have a copy of UL486C, and voltage is just
specified for dielectric testing. That standard specifies tests with AC,
because it is easier (and cheaper) to generate and ramp up compared to DC,
and DC test platforms are relatively rare.
So my interpretation of UL486C is that because of AC voltage peaks compared
to RMS (Vpeak = Vrms x 1,414), a 1000VAC rated connector under UL486C would
need to be tested to 1414VDC. Working that math backwards, a 600VAC rating
would mean the DC dielectric rating would be equivalent to 424.33 VDC.
How that would apply to AHJs asking you questions, I do not know!
Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
d <dan.fink at greendustrialtraining.com>anbob88 at gmail.com
970-672-4342
On Fri, May 7, 2021 at 3:43 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
In another thread these connectors were discussed recently. There was a
question regarding the suitability for DC circuits. I don't think we came
up with any answers or consensus on that. I see the connectors are UL
listed to the 486C standard. I can't determine whether that is applicable
to AC and DC circuits. Does anyone know?
I have only used these on AC circuits and they have been very effective.
Now I'm curious whether they can be used on DC circuits up to 600 volts.
While on the subject, I noticed they are UL 467 listed for grounding and
bonding. That's helpful where you have EGC splices for conductors up to #10
AWG inside junction boxes.
Jason Szumlanski
Florida Solar Design Group