What happens when the contactor fails? I don't trust a NC contactor that is
supposed to open on 240Vac coil voltage from the generator. It's not a
failsafe solution.
Jason
On Tue, May 4, 2021, 3:15 PM Drake <drake.chamberlin at redwoodalliance.org>
wrote:
> P.S. The contactor method is even mentioned somewhere in the Outback
> literature. I've been using it for years. It is very simple and requires no
> complex equipment. It will not interfere with rapid shutdown. 40 A, 240 V
> contactors with 240 V coils are readily available and not terribly
> expensive. The 240 V output of the generator circuit provides the signal.
>
> At 10:02 AM 5/4/2021, you wrote:
>
> Get a contactor with a 240 VAC coil. Connect the coil wire wires to the
> 240 V output circuit of the generator, so when the generator comes on, the
> contactor opens. Run the current from the AC coupled Enphase inverters
> through the contacts from common to N/C.
>
> ---
>
>
>
> On 2021-05-03 10:26, Dave Tedeyan wrote:
>
> Hi All,
>
> I am planning on using a Sol-Ark for the first time for adding battery
> backup to an existing system. It is Enphase, so clearly it will be AC
> coupled, and there is a whole house generator. When I talked to Sol-Ark
> about it, they recommended putting the generator on a time of use schedule
> to not allow it to come on during the day so that we don't run into the
> issue of the solar backfeeding the generator.
>
> I was wondering though if anyone has just used a contactor to cut out the
> solar when the generator turns on? Something like Outback's GS-AC-Gen-Kit,
> although in this case I will need something rated for just over 30A. This
> seems like a better way to allow the generator to run at any time it is
> needed, especially if it is a gloomy, snowy, winter day.
>
> Cheers,
> Dave
>
> --
>
> *Dave Tedeyan, PE * [image: Sungineer Solar]
> 1653 Slaterville Road, Ithaca, NY 14850
> Cell: 607-288-2898
> www.sungineersolar.com
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210504/98330d4c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 78c218.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210504/98330d4c/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 78c218.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210504/98330d4c/attachment-0001.gif>
More information about the RE-Wrenches
mailing list