Glenn Burt glenn.burt at glbcc.com
Mon May 3 22:19:05 EDT 2021


We have a couple of off-grid systems (not SolArk) where we put a Dwyer current sensing relay on the output from the generator, energizing a Gigavac, DC relay that opens the combined PV output circuit and it works well.

Not exactly what you are looking for, but the principal would be the same.

 

-Glenn

 

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Dave Tedeyan
Sent: Monday, May 03, 2021 10:27 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Generator and AC coupling on a Sol-Ark

 

Hi All, 

 

I am planning on using a Sol-Ark for the first time for adding battery backup to an existing system. It is Enphase, so clearly it will be AC coupled, and there is a whole house generator. When I talked to Sol-Ark about it, they recommended putting the generator on a time of use schedule to not allow it to come on during the day so that we don't run into the issue of the solar backfeeding the generator.

 

I was wondering though if anyone has just used a contactor to cut out the solar when the generator turns on? Something like Outback's GS-AC-Gen-Kit, although in this case I will need something rated for just over 30A. This seems like a better way to allow the generator to run at any time it is needed, especially if it is a gloomy, snowy, winter day.

 

Cheers, 

Dave

 

-- 

Dave Tedeyan, PE

  <http://sungineersolar.com/wp-content/uploads/2019/08/Sungineer-Logo-1.png> 

1653 Slaterville Road, Ithaca, NY 14850

Cell: 607-288-2898

 <http://www.sungineersolar.com/> www.sungineersolar.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210503/c93431f6/attachment.htm>


More information about the RE-Wrenches mailing list