[RE-wrenches] MC4s are listed for THWN, right?
Ray
ray at solarray.com
Thu Apr 29 11:41:02 EDT 2021
I have been busted by inspectors for "modifying a UL device in a way
that is not permitted in its listing", or something like that. While
weep holes make all the sense in the world, and I have commonly seen
1/4" holes drilled in LBs for ground wires, etc; one out of ten AHJs
might not like it.
Ray Walters
Remote Solar
303 505-8760
On 4/29/21 9:43 AM, frenergy wrote:
> Eric,
>
> I like your idea of drilling the weepage holes as long as
> they are not big enough to allow critters like wasps to make a home
> inside the J-box. We will use aluminum tape on unused mounting holes
> in the back of the box for the same reason. Lurkers welcome.
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
> On 4/28/2021 6:19 PM, ericstev at vermontel.net wrote:
>>
>> Wrenches,
>>
>> I am normally a lurker on the List, but I would like to add a fact
>> observation and a personal preference to the topics raised by this
>> discussion.
>>
>> First, THWN does have PVC as its primary insulation, but it is
>> sheathed in Nylon which is a polyamide plastic. Therefore the
>> compatibility with MC4 connectors should be polyamide being squeezed
>> by the restraining bushing in the MC4, not PVC.
>>
>> I prefer Buchanan copper crimp connectors when splicing PV wire to
>> THWN-2 in a roof junction box. The bared wires should be lightly
>> doped with NO-OX-ID A-Special grease
>> https://www.sanchem.com/electrical-contact-lubricant.html
>> <https://www.sanchem.com/electrical-contact-lubricant.html> before
>> sleeving and crimping with the crimp sleeve to repel entry of
>> moisture and corrosive gasses into the wire joint. I consider the
>> crimped joint to be superior to any screw-clamped joint that would be
>> made in a Polaris style connector. I also drill weepage holes in the
>> bottom corner of the junction box to mitigate any collection of water.
>>
>> Eric Stevens, Vermont Made Energy
>>
>>
>