Keep in mind that 7.5kW is max charge/discharge for 10 sec...it is NOT the
continuous rate. This comes into play in the following scenario:
Let’s say a single Powerwall 2 is at 50% SOC and there is a utility outage
on a sunny day. The inverter is outputting 7kW AC and loads in the house
are below 2kW. The Powerwall will force the PV inverter to turn off via
frequency shift and the inverter sit in a holding pattern, trying to
reconnect every 5 minutes. If PV continues to be above 5 kW, then it will
be turned off until the battery shuts off at its designated cut off %. Not
an ideal scenario. This is why I like to use 5kW of PV per Powerwall as a
general rule, to avoid this worst case scenario.
Best,
Chris
On Sun, Apr 18, 2021 at 1:53 PM Barton Churchill <bchurchill at energy-1.net>
wrote:
> You can just land the new PV to the same "generation" panel that already
> hosts the 3 Powerwalls and existing PV inverter output breakers. There
> should be no loads on this panel. The Powerwall AC coupled solar limit is
> 7.5 KW AC per Powerwall, note AC not DC. The DC rating is irrelevant here.
> If the combined PV AC inverter output is less than 22.5 kW the system will
> work fine. Tesla does have a list of approved PV inverters but unless
> you're looking to connect something over 3 years old it should be fine.
>
> *Barton Churchill*
> *Director, Power Division*
> 2042 Stadium Drive Suite 2 • Bozeman, MT 59715
> <https://www.google.com/maps/search/2042%0D%0A+Stadium+Drive+Suite+2+%E2%80%A2+Bozeman,+MT+59715?entry=gmail&source=g>
> • (O) 406-587-2917 • (D) 406-589-4493
> 235 E. Broadway • Jackson, WY 83001 • (O) 307-200-2210
> bchurchill at energy-1.net <blansing at energy-1.net> | www.energy-1.net
>
> ------------------------------
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf
> of Kirk Herander, VSE <kirkh at vermont.solar>
> *Sent:* Friday, April 16, 2021 9:13 AM
> *To:* re-wrenches at lists.re-wrenches.org <re-wrenches at lists.re-wrenches.org
> >
> *Subject:* [RE-wrenches] Powerwall 2 AC PV regulation
>
> Hello all,
> I am adding more PV to an orphaned Powerwall 2 AC system (which is all new
> to me), -3- PW's stacked to total about 40kwh of usable storage. it
> presently has about 13kw of PV, though -2- SMA inverters, feeding into it
> through a common subpanel between the PW gateway and the main panel. I'm
> wondering if there is a limit to the amount of PV the powerwall can
> regulate/backoff (or use for battery charging) during a utility outage.
> What is the max PW charge rate? I need to add about 10 kw of PV to produce
> the owners goal of 100% coverage of electrical demand.
> If necessary for safety, i assume the extra pv inverter can be routed to
> the main panel, and then won't participate in battery charging if the grid
> goes down. Am I correct? Thanks. The PW manuals are of little use here.
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 30th Anniversary 1991-2021!!*
>
> *www.vermont.solar*
> <https://us-west-2.protection.sophos.com?d=outlook.com&u=aHR0cHM6Ly9uYW0wMi5zYWZlbGlua3MucHJvdGVjdGlvbi5vdXRsb29rLmNvbS8_dXJsPXd3dy52ZXJtb250c29sYXJub3cuY29tJmRhdGE9MDIlN0MwMSU3QyU3QzlmMDMzMGQ3NWEyNDQ4NzAxMTI0MDhkNjg1MzExODQxJTdDODRkZjllN2ZlOWY2NDBhZmI0MzVhYWFhYWFhYWFhYWElN0MxJTdDMCU3QzYzNjg0Mjg0MzIzMzQ3NzY0NSZzZGF0YT0wTmp5dUtlUWJFSzYyNDVTTm5rOFg0WG5QOVElMkIlMkJxdHZjQUxrZERnaHZrNCUzRCZyZXNlcnZlZD0w&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=T0V4VmVuWVp1a3A2UUVZOTRNRitLRWViVk1TM1o4Wll0MDNtSTg5WndOTT0=&h=257d32539c424fbdb09425b1e02ea242>
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo
C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210418/ee6154b5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-fj0ah4gy.png
Type: image/png
Size: 7692 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210418/ee6154b5/attachment.png>
More information about the RE-Wrenches
mailing list