[RE-wrenches] Powerwall 2 AC PV regulation
Glenn Burt
glenn.burt at glbcc.com
Sat Apr 17 19:56:27 EDT 2021
The manuals I have say 7.6kW(AC) per PW2
Glenn
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Jason Szumlanski
Sent: Friday, April 16, 2021 9:46 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Powerwall 2 AC PV regulation
I think the limit is now stated as 7.6kw if memory serves me right.
Jason
On Fri, Apr 16, 2021, 12:11 PM Matt Partymiller <matt at sesre.com <mailto:matt at sesre.com> > wrote:
They used to advocate 7.9kW AC/DC per Powerwall. That number may have gone down recently. Coupling an inverter on the line side of the backup gateway will resolve your issue of meeting homeowner demand. Tesla will want you to add a CT to that inverter to ensure it does not mess up their monitoring system, though that may already be incorrectly configured and not monitoring the whole home if the system is backup only.
Matt
Matt Partymiller
General Manager
Solar Energy Solutions, LLC
Lexington | Louisville | Bloomington | Cincinnati | Evansville | Indianapolis
859-312-7456 (Office)
877-312-7456 (General)
matt at sesre.com <mailto:matt at sesre.com>
Check out our amazing new website and social media updates: www.sesre.com <http://www.sesre.com/>
<http://www.sesre.com/> <https://www.facebook.com/SolarEnergySolutionsLLC> <https://www.instagram.com/solarenergysols> <https://twitter.com/SolarEnergySols> <https://www.linkedin.com/company/sesre>
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org> > On Behalf Of Kirk Herander, VSE
Sent: Friday, April 16, 2021 11:13 AM
To: re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Powerwall 2 AC PV regulation
Hello all,
I am adding more PV to an orphaned Powerwall 2 AC system (which is all new to me), -3- PW's stacked to total about 40kwh of usable storage. it presently has about 13kw of PV, though -2- SMA inverters, feeding into it through a common subpanel between the PW gateway and the main panel. I'm wondering if there is a limit to the amount of PV the powerwall can regulate/backoff (or use for battery charging) during a utility outage. What is the max PW charge rate? I need to add about 10 kw of PV to produce the owners goal of 100% coverage of electrical demand.
If necessary for safety, i assume the extra pv inverter can be routed to the main panel, and then won't participate in battery charging if the grid goes down. Am I correct? Thanks. The PW manuals are of little use here.
Kirk Herander / kirkh at vermont.solar <mailto:kirkh at vermont.solar>
Owner|Principal, VT Solar, LLC
Celebrating our 30th Anniversary 1991-2021!!
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0> www.vermont.solar
dba Vermont Solar Engineering
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210417/77ab9d88/attachment.htm>
More information about the RE-Wrenches
mailing list