[RE-wrenches] Odd inspection procedure
Will White
will at solarenergy.org
Mon Apr 5 09:40:08 EDT 2021
William,
I've never had an AHJ request pictures in lieu of a physical inspection but
I've personally performed many inspections as a third-party inspector using
photos. As long as you have quality pictures a good inspector can find most
major issues. The key is having good photos of the proper equipment. At the
very least they should be able to identify when a physical inspection is
necessary.
I'm all for remote inspections which saves time and money for everyone
involved.
Thanks,
Will
On Wed, Mar 31, 2021 at 1:37 PM William Miller <william at millersolar.com>
wrote:
> Friends:
>
>
>
> We just finished a grid-tied project
> <https://millersolar.com/MillerSolar/Portfolio/Rework/BIG-SUR-SERVICE/Big_Sur_Service_Upgrade.html>
> that included a pretty complicated service upgrade. The project is in
> Monterey County, California. The site is pretty remote on the south end of
> the Big Sur coastline and Highway 1 is closed (as is not uncommon) to the
> north with a washout. This makes it time consuming for an inspector to
> reach the site, but even without the washout the travel time is measured in
> hours.
>
>
>
> Days in advance we scheduled the final inspection on the building
> department web-site as is SOP and were awarded a slot for yesterday.
> Yesterday morning an inspector called at 7:30 AM to announce they were too
> busy to make the appointment. Instead I was directed to take a series of
> photographs to verify the validity of our installation work. Below is the
> list they provided. Note how vague the requirements are, particularly the
> fifth one. I was told that this process will be standard operation
> procedure for the County of Monterey in the near future for solar
> installs.
>
>
>
> This seems wrong to me. I can’t believe that any collection of
> photographs can accurately portray if even the most simple photovoltaic
> system, let alone one with a 300 amp CT service and 400 amp transfer
> switch, is installed correctly. I know in the 1980s the solar water
> heating industry had acquired a collective black-eye due to shoddy
> installation procedures and I fear this is where the PV industry may be
> headed.
>
>
>
> I submitted a handful of photos and was granted a final approval. I have
> very mixed feelings about this “success.” I feel like I cheated on a
> test.
>
>
>
> I am curious if any of you have had a similar experience to this. As
> always I am informed and sometimes amused by what I learn on this forum.
>
>
>
> List of requested photographs:
>
>
>
> ☐ PV module model number, quantity, and location according to the
> approved plan.
>
> ☐ Roof penetrations flashed/sealed according to the approved plan.
>
> ☐ Array exposed cables are properly secured, supported, and routed to
> prevent physical damage.
>
> ☐ Grounding/bonding of rack and modules according to the manufacturer’s
> installation instructions.
>
> ☐ Equipment installed, listed and labeled according to the approved plan
> (e.g., PV modules, dc/dc converters, combiners, inverters, rapid shutdown
> equipment).
>
> ☐ Overcurrent devices are the type and size according to the approved
> plan.
>
> ☐ Disconnects according to the approved plan and properly located as
> required by the NEC.
>
> ☐ PV system markings, labels and signs according to the approved plan.
>
> ☐ Connection of the PV system to the grounding electrode system according
> to the approved plan.
>
> ☐ Access and working space for operation and maintenance of PV equipment
> such as inverters, disconnecting means and panelboards (not required for
> PV modules) [NEC 110.26].
>
> ☐ The rapid shutdown system is installed and operational according to the
> approved plan [NEC 690.12].
>
>
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
*Will White*
Curriculum Developer
e: will at solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installation Professional
# 093006-34