Then just as a follow up, I looked at the SMA-41 datasheet. This shows that
it runs at it's highest efficiency when the  output power / rated power is
about 0.4 to 0.6, and the only real loss in efficiency comes when you are
running at about 0.1 and below.

On Wed, Mar 3, 2021, 8:35 PM Dave Tedeyan <dtedeyan at taitem.com> wrote:

> I've never really trusted PVWatts on this. I just did a quick test using
> my location in the northeast, with all the standard values and then just
> changing the DC to AC ratio. It's telling me that a ratio of 1.5 is almost
> exactly the same as a ratio of 1, and that around 1.3 is best. You actually
> lose about 2% at 0.5 and about 8% production at a ratio of 2.
>
> So I can only conclude that either PVWatts does not have a great
> calculation, or the efficiency loss due to not running the inverter at
> rated power is worse than I assumed.
>
> Cheers,
> Dave
>
> On Wed, Mar 3, 2021, 6:14 PM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>> I've used that document many times when clients question the ratio. I
>> wish I knew exactly how the PVWATTS ratio calculation worked. I know
>> there's information on how this is all done, but I don't really have the
>> time or inclination to study it. I'm wondering if someone knows how
>> accurate It is.
>>
>> On Wed, Mar 3, 2021, 4:04 PM Jay <jay.peltz at gmail.com> wrote:
>>
>>> Emphase has a white paper showing production vs module size and
>>> locations around the country.
>>>
>>> I don’t know if it’s more accurate than pv watts but you might check it
>>> out.
>>>
>>> Jay
>>> Peltz power.
>>>
>>> On Mar 3, 2021, at 12:13 PM, Jason Szumlanski <
>>> jason at floridasolardesigngroup.com> wrote:
>>>
>>> 
>>> I'm wondering how accurate the DC to AC ratio is when using PVWATTS. I
>>> did a quick PVWATTS analysis at my local area using a typical commercial
>>> roof tilt and found that using a 420W module on an IQ7A versus a 385W
>>> module on an IQ7+ yields almost identical results. The 420W module has 1%
>>> less annual production at to the 145% ratio compared to the 132% ratio with
>>> the 385W module.
>>>
>>> Given that, I can't imagine why anyone would use the IQ7A versus the
>>> IQ7+ on a 208V system. Why incur the additional cost if the AC output
>>> current is identical for both inverters?
>>>
>>> If PVWATTS is right, I guess it's a non-issue in my local area, but it
>>> may vary in other locations where clipping is more common. The heat here
>>> results in little clipping at a 132% ratio here, and I guess at 145% the
>>> morning and afternoon advantages largely outweigh the mid-day clipping
>>> increase.
>>>
>>> Jason Szumlanski
>>>
>>>
>>>
>>> On Tue, Mar 2, 2021 at 10:00 AM Jason Szumlanski <
>>> jason at floridasolardesigngroup.com> wrote:
>>>
>>>> I was surprised to learn that the IQ7A is limited to 290 W continuous
>>>> at 208 volts. That pretty much puts Enphase out of the running for light
>>>> commercial jobs with new high-powered 72 cell panels. Any thoughts on this?
>>>>
>>>> Jason
>>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210303/f6fb32fc/attachment.htm>


More information about the RE-Wrenches mailing list