[RE-wrenches] Small, non-Tesla GTBB system design
John Blittersdorf
john.blittersdorf at gmail.com
Wed Mar 3 07:10:36 EST 2021
William,
I agree with you with Radian, Fortress and just add a subpanel identical
to the main grid panel as close possible. Put all critical loads on sub and
larger loads on grid panel. Being side by side, swapping circuits is easy.
I also install an iota charger for generator redundancy. OpticRE works
great for monitoring.
John Blittersdorf
On Wed, Mar 3, 2021 at 1:19 AM William Miller <william at millersolar.com>
wrote:
> Friends:
>
>
>
> I am getting asked more often to provide design for grid-tied battery
> backup systems. I generally try to talk clients out of battery backup
> because I have always felt that the grid is the greenest battery and that
> the grid reliability is better than one might remember. However, with
> climate change and media attention, the need and market pressure is
> becoming stronger.
>
>
>
> I am really interested in what others have created in the way of solutions
> to this question. I have thought about it a lot. If its ok, I’d like to
> free-associate about some of my concerns and conclusions then ask if any of
> you are willing to share your ideas on how best to fill this need. Here
> goes:
>
>
>
> I am a firm believer in segregate load delivery for these reasons:
>
> 1. To back up an entire grid service you have to, in good conscience,
> perform a thorough load study and provide enough through-transfer to
> provide for maximum load conditions during grid up-time. The backup system
> cannot be a supply bottle-neck.
>
> 2. I don’t accept manual load-shedding for one moment. What if the AC
> and the dryer are running when the grid goes out? The system crashes.
>
> 3. In a home with whole-house backup, it is difficult for the consumer
> to know there is an outage and to conserve. Cellphone notification
> features are now more common, but cell phone batteries die and phones get
> left in the other room with the ringer off, so it is possible for
> homeowners to leave consumptive loads on after the grid goes down.
>
>
>
> Conclusion: With segregated loads, the transfer, inverter and storage can
> be scaled down and the reliability increases. Less cost, better
> performance.
>
>
>
> So given that the system sizing will be modest, has anyone come up with a
> reasonable design using standard, grid-sell capable battery inverters?
>
>
>
> Here is how I am imagining such a system:
>
>
>
> I see a modest battery system with a 4 to 8 KW inverter, DC coupled PV and
> a matching no-maintenance battery system. It would have these components:
>
>
>
> Inverter: Must have a dedicated generator and grid input and good remote
> monitoring, robust web interface and email notification. Outback Radian.
>
>
>
> Batteries: Gel or lithium. I have a client that has been grid-floating a
> set of MK Powered gel batteries since 1999. Or a Blue Planet or Fortress
> cabineted system.
>
>
>
> Generator: Small pad-mount natural gas or propane fueled generator or a
> portable gas powered unit with stabilized gas. If the generator is
> portable, provide an AC flanged inlet and sturdy cord long enough so
> generator can be 10 feet from any opening in the home. Provide durable
> signage on the generator indicating CO safety practices.
>
>
>
> PV: DC coupled for simplicity. Sized based on annual energy needs, not on
> critical loads. Grid power is likely to go down in the stormy winter
> months or smoky fire season, so PV is not a reliable energy source during
> grid outages.
>
>
>
> AC Distribution: Segregated loads with at least one commonly used
> lighting circuit not on the critical loads panel so the homeowner soon
> realizes the power is out.
>
>
>
> Unless you are a Tesla dealer, I am sure many of you have gone through the
> same mental acrobatics trying to figure out the best solution to this
> design request. I am very interested in what the rest of you may have come
> up with.
>
>
>
> Thanks in advance.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
> <https://www.google.com/maps/search/17395+Oak+Road,+Atascadero,+CA+93422?entry=gmail&source=g>
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210303/d90a3511/attachment.htm>
More information about the RE-Wrenches
mailing list