[RE-wrenches] Small, non-Tesla GTBB system design

William Miller william at millersolar.com
Wed Mar 3 00:41:59 EST 2021


Friends:



I am getting asked more often to provide design for grid-tied battery
backup systems.  I generally try to talk clients out of battery backup
because I have always felt that the grid is the greenest battery and that
the grid reliability is better than one might remember.  However, with
climate change and media attention, the need and market pressure is
becoming stronger.



I am really interested in what others have created in the way of solutions
to this question.  I have thought about it a lot.  If its ok, I’d like to
free-associate about some of my concerns and conclusions then ask if any of
you are willing to share your ideas on how best to fill this need.  Here
goes:



I am a firm believer in segregate load delivery for these reasons:

1.   To back up an entire grid service you have to, in good conscience,
perform a thorough load study and provide enough through-transfer to
provide for maximum load conditions during grid up-time.  The backup system
cannot be a supply bottle-neck.

2.   I don’t accept manual load-shedding for one moment.  What if the AC
and the dryer are running when the grid goes out?  The system crashes.

3.   In a home with whole-house backup, it is difficult for the consumer to
know there is an outage and to conserve.  Cellphone notification features
are now more common, but cell phone batteries die and phones get left in
the other room with the ringer off, so it is possible for homeowners to
leave consumptive loads on after the grid goes down.



Conclusion:  With segregated loads, the transfer, inverter and storage can
be scaled down and the reliability increases.  Less cost, better
performance.



So given that the system sizing will be modest, has anyone come up with a
reasonable design using standard, grid-sell capable battery inverters?



Here is how I am imagining such a system:



I see a modest battery system with a 4 to 8 KW inverter, DC coupled PV and
a matching no-maintenance battery system. It would have these components:



Inverter:  Must have a dedicated generator and grid input and good remote
monitoring,  robust web interface and email notification.  Outback Radian.



Batteries:  Gel or lithium.  I have a client that has been grid-floating a
set of MK Powered gel batteries since 1999.  Or a Blue Planet or Fortress
cabineted system.



Generator:  Small pad-mount natural gas or propane fueled generator or a
portable gas powered unit with stabilized gas.  If the generator is
portable, provide an AC flanged inlet and sturdy cord long enough so
generator can be 10 feet from any opening in the home.  Provide durable
signage on the generator indicating CO safety practices.



PV: DC coupled for simplicity.  Sized based on annual energy needs, not on
critical loads.  Grid power is likely to go down in the stormy winter
months or smoky fire season, so PV is not a reliable energy source during
grid outages.



AC Distribution:  Segregated loads with at least one commonly used lighting
circuit not on the critical loads panel so the homeowner soon realizes the
power is out.



Unless you are a Tesla dealer, I am sure many of you have gone through the
same mental acrobatics trying to figure out the best solution to this
design request.  I am very interested in what the rest of you may have come
up with.



Thanks in advance.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985