[RE-wrenches] grid-tie solar behind a generator

Brett Bartmasser brettbartmasser at gmail.com
Sun Feb 28 15:40:09 EST 2021


We have installed relays that distinguish between generator and grid power.
They simply go in-between the solar and the service. They disconnect when
the gen runs and reconnect when the grid comes back. They have worked so
far as I know.

On Sun, Feb 28, 2021 at 12:32 PM Benn Kilburn <benn at skyfireenergy.com>
wrote:

> I had a similar scenario a few years ago and looked at the Generac SSM,
> but for some reason(s) I cannot recall, could not go this route.
> The system was on a house and the auto transfer switch and generator were
> in a shack that was unreasonable to trench too, and we did not want to rely
> on a wireless option.
>
> The solution we came up with was a contact that would disconnect the
> inverters from the house panelboard upon a loss of voltage (grid).
> Unfortunately we did not come up with a solution that would automatically
> reconnect the inverters once the grid was restored... because we couldn’t
> reliably distinguish between the generator and the grid, so it required a
> manual reset once the customer could confirm they had grid power and not
> running off the generator.
> The client said they often did not know that there was a power outage so
> there could be times they would not even know the inverters had shut off...
> so I ran a low voltage line to a LED light in their kitchen area that
> would come on upon loss of grid and would go out when the inverters were
> manually reset.
>
> Benn Kilburn
> SkyFire Energy
> 780-906-7807
>
> On Feb 25, 2021, at 6:40 AM, Nik Ponzio, Building Energy <
> nponzio at buildingenergyus.com> wrote:
>
> We are installing 25kW of PV on a service with an existing backup
> generator (Eaton 30KW) and auto transfer switch. Because of the remote
> location of the generator and transfer switch, we can not easily connect on
> the grid-side of the transfer switch as we usually do (without cutting a
> very long trench.) So we're looking for a way to lock out the solar during
> generator use. And then, ideally, reconnect the solar automatically when
> the grid is restored.
>
> Is there an off-the-shelf product available at this point to accomplish
> this?
>
> I see a thread on here
> <https://mailtrack.io/trace/link/7643522e54e5bd30057d2e139c7b93d1c488b655?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmsg23906.html&userId=6273276&signature=c4db635fbd2d1225>
> from a couple years ago that recommended the Generac SMM for this type of
> scenario. Any current thoughts on this approach?
>
> Any suggestions would be appreciated.
>
>
> --
> Nik Ponzio
> Building Energy
> 1570 South Brownell Road
> Williston, VT 05495
> direct: 802-318-7003
> nponzio at buildingenergyus.com
> http://www.BuildingEnergyVT.com
> <https://mailtrack.io/trace/link/058e994a3bba9674653a69dd2a6976e0914d2761?url=http%3A%2F%2Fwww.BuildingEnergyVT.com&userId=6273276&signature=8b5247886585b42b>
>
>
>
> "Building Solutions for a Sustainable Future"
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210228/0c6218d3/attachment.htm>


More information about the RE-Wrenches mailing list