[RE-wrenches] Battery Specific Gravity versus Electrolyte Level

Dana Orzel dana at solarwork.com
Tue Feb 9 15:51:07 EST 2021


My recommendation on the HUPS that I install are:

 

Use a refractometer!

 

Check your SG, & compare all cells & if highest to lowest – If 0.02 or less no need to EQ.

                             If 0.04 or greater time to EQ.

I water every 8 weeks with a pump watering system, winter about 2-3 gallons per  2 months summer 4-4.5 gallons per 2 months.

 

IMHO – EQ is rough on most batteries & this recommendation from NWES  almost 30+ years ago has served me very well.

 

I have many clients that have gotten 23+ years on their HUPS. I use them & I have only had to EQ once a year for 4years.

2500 AHR @48 VDC on 6000 watts tracked in a narrow N/S canyon, 4 hours of direct sun Nov 25-Jan 25.

 

 

Dana Orzel                              Great Solar Works, Inc. 

C - 208.721.7003                       dana at solarwork.com

Idaho Contractor - # 028765         Idaho PV # 028374

NABCEP # 051112-136                       www.solarwork.com <http://www.solarwork.com/> 

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Dave Angelini Offgrid Solar
Sent: Tuesday, February 9, 2021 1:09 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Battery Specific Gravity versus Electrolyte Level

 

A main point to the choir is that each manufacturer has their own recommendations. The US battery I often use has monthly EQ.

Looking at 30 years of batteries here and the Offgrid manufactures seem to change what they like over time. Sometimes it is so complicated that I can't expect my client to succeed. I dumb it down,  just the basics, and they still get 10 years or more on a set of L16's.
 
I think it is because battery companies are in the business of selling batteries. I appreciate that also! 
 
This is not rocket science though, If I had them do all of the things on that list, well, they would not listen to me on the basics.
 
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net <mailto:offgridsolar at sti.net> 
text 209 813 0060
 
On Tue, 9 Feb 2021 14:29:12 -0500, Ray <ray at solarray.com <mailto:ray at solarray.com> > wrote:
> Dave makes a good point; I also don't recommend opening the cells while 
> they are charging at a high rate.   I like to get SG readings with the 
> electrolyte being mixed by bubbling, but I turn off the charging 
> sources, and let it settle down for a few minutes, before opening caps.
> 
> And I second Steve's comments: over charging and over filling the cells 
> can both lead to more problems than EQing might solve.
> 
> Ray Walters
> Remote Solar
> 303 505-8760
> 
> On 2/9/21 10:35 AM, Dave Angelini Offgrid Solar wrote:
>> That does not sound  best to me. I get the point but there are much
>> better
>> ways. Not good for you to be close around a bank in EQ. If you are
>> checking
>> water level every month the level should not be really low. You do this
>> in
>> case you miss a cell a month back! You should be counting as the water
>> goes
>> in to see if you have put about the same amount in. I have never noticed
>> any advantage to mixing the cells after watering. They will get mixed the
>> next day. If this concerned you, you could run a 30 minute absorb after
>> watering.
>> 
>> I like to EQ before watering so my customer does not over fill and start
>> the corrosion process. Just open all of the cells and look before they
>> EQ.
>> 
>> I also like to mark 2 of the lower SG cells and 2 of the good ones. This
>> makes it easier for my clients to check the bank. Once every summer or 2
>> they need to look at all of the cells. Summer is best because it is the
>> time when you can do long corrective EQ's if you find trouble.
>> 
>> 
>> Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/
>> e-mail offgridsolar at sti.net <mailto:offgridsolar at sti.net> 
>> text 209 813 0060
>> 
>> On Tue, 9 Feb 2021 05:36:39 -0800, Mark Frye <markf at berkeleysolar.com <mailto:markf at berkeleysolar.com> >
>> wrote:
>>> My Rolls manual says:
>>> 
>>> "It is recommended to water the battery cells half way through the
>>> equalization. This is to
>>> assure the water is completely mixed into the electrolyte."
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try
>> the
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210209/002445c1/attachment.htm>


More information about the RE-Wrenches mailing list