My experience and advice from Tech Support at Fortress was NOT to network
the eVault 18.5 with only 2 batteries. We just installed two eVault18.5
with one Sol-Ark12K. The communication doesn't work properly with only two
batteries. The tech advised to run both batteries independently as Masters,
which was the only way we could make it work. All attempts at networking
them failed. We didn't try to network the batteries to the inverter.
Of course, Murphy's Law dictated that this was a remote system with no
internet or cell reception. So, I had to make a second trip out to make it
work after I found this out from Tech Support the next morning.
Apparently you can network one battery with the Sol-Ark in closed loop but
the tech I talked to said how this is done (special com cable) varies with
the version of the Sol-Ark one is using since Sol-Ark has been making
changes to their circuit board.
Eric Smiley, MASc
Project Manager, North Island
E: eric at vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca <http://www.viridianenergy.ca>
<http://www.viridianenergy.ca/>
RENEWABLE POWER NOW
On Mon, 1 Feb 2021 at 14:01, Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> I think this was mentioned by others, but Fortress confirmed to me today
> that closed loop only works with one or two evault batteries with Sol-Ark.
> More than that and communications breaks down. They're working on a fix,
> but they told me that there are no guarantees. They could not give me a
> date. It sounded like it was a hardware fix and existing batteries would
> not be upgradable.
>
> Jason
>
> On Mon, Feb 1, 2021, 2:22 PM Chris Sparadeo <sparadeo.chris at gmail.com>
> wrote:
>
>> Hi Jay,
>>
>> Yes, when installed in a closed loop configuration, the Sol Ark uses the
>> SOC% provided by the BMS...which can be used to control the AGS.
>>
>> On Mon, Feb 1, 2021 at 1:58 PM Jay <jay.peltz at gmail.com> wrote:
>>
>>> Thx Chris.
>>>
>>> Does the sol ark use the % info from the batteries for ags operation?
>>>
>>> Jay
>>>
>>> On Feb 1, 2021, at 10:10 AM, Chris Sparadeo <sparadeo.chris at gmail.com>
>>> wrote:
>>>
>>>
>>>
>>> Jay,
>>>
>>> I have installed the eFlex paired with Sol Ark and it was very straight
>>> forward. You need to make a modified RJ45 cable, but other than that, it’s
>>> pretty much plug and play. I believe that Fortress is still working on
>>> their WiFi monitoring for the eFlex...They say the eVault will be closed
>>> loop by Q2.
>>>
>>> -Chris
>>>
>>> On Mon, Feb 1, 2021 at 11:56 AM Dave Angelini Offgrid Solar <
>>> offgridsolar at sti.net> wrote:
>>>
>>>> Jay,
>>>>
>>>> I worked with them on the XW to close the loop. They did get it working
>>>> with Eflex and it is easy to commission. However, they were not able to
>>>> get
>>>> the conext insight data out to the cloud totally implemented. Until they
>>>> prove that to me, I will stay with Discover AES. The site at the bottom
>>>> showing state of charge is an AES battery BTW.
>>>>
>>>>
>>>> Dave Angelini Offgrid Solar
>>>> "we go where powerlines don't"
>>>> http://members.sti.net/offgridsolar/
>>>> e-mail offgridsolar at sti.net
>>>> text 209 813 0060
>>>>
>>>> On Mon, 1 Feb 2021 08:43:03 -0700, jay <jay.peltz at gmail.com> wrote:
>>>> > Some questions to those installing fortress power.
>>>> >
>>>> > 1. has anyone installed them in a closed loop comm and if so, which
>>>> > inverter
>>>> >
>>>> > 2. it doesn’t appear that there is any online or app for
>>>> > communication/monitoring?
>>>> >
>>>> > thx
>>>> > jay
>>>> > _______________________________________________
>>>> > List sponsored by Redwood Alliance
>>>> >
>>>> > List Address: RE-wrenches at lists.re-wrenches.org
>>>> >
>>>> > Change listserver email address & settings:
>>>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> >
>>>> > There are two list archives for searching. When one doesn't work, try
>>>> the
>>>> > other:
>>>> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> >
>>>> > List rules & etiquette:
>>>> > http://www.re-wrenches.org/etiquette.htm
>>>> >
>>>> > Check out or update participant bios:
>>>> > http://www.members.re-wrenches.org
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> --
>>> Chris Sparadeo
>>>
>>>
>>> C_802-369-4458
>>> H_802-728-3059
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> --
>> Chris Sparadeo
>>
>>
>> C_802-369-4458
>> H_802-728-3059
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210201/cd254556/attachment.htm>
More information about the RE-Wrenches
mailing list