Aloha All,

I just had a plan reviewer kick out our plans for this very reason!
Sol-Ark 12kw mounted above a Blue Ion 2.0 cabinet. Lucky on this job I have
the space to offset the 2 pieces of equipment so I didn't push back at all.
But it will definitely be a problem in a lot of future installs. Not to
mention aesthetically it doesn't look very neat and tidy.

I am think that the wording of 110.26(E) (1) (a) and 110.26(E) (2) (c)  may
be my ticket:
"No piping, ducts, leak protection apparatus, or other equipment foreign to
the electrical installation shall be located in this zone"

I have to think that the battery is not foreign to the electrical
installation.

Any thoughts?

Aloha,

Lou Russo
(808) 345 6762



On Sun, Jan 31, 2021 at 12:59 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:

> I'm reading that the working space must be down to the floor/grade with
> the exception of other equipment extending up to 6 inches deeper than the
> enclosure for which the working space applies.
>
> For example, technically you can't put a 32 inch deep base cabinet and
> countertop below a load center. I see it all the time, but inspectors
> around here in some jurisdictions will not allow it.
>
> I seriously doubt I would be flagged for a 24 inch deep battery enclosure
> below a 12 inch deep inverter with integrated disconnects, but by the book
> it seems like a violation.
>
> Jason
>
>
> On Sun, Jan 31, 2021, 5:38 PM Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
>>    l dont know that this NEC code applies in the way you are reading or
>> understanding it, I do see where foreign components are restricted with in
>> the space. We have systems with two or three outback radians above
>> blueplanet batteries and have not seen an issue. The BPE's are in an
>> enclosed cabinet fire approved and protected from shock, putting batteries
>> further away will create space issues. Since all of these components are
>> required for the "system" to operate they are necessary.
>> Jerry
>>
>> On Sun, Jan 31, 2021, 12:28 PM Jason Szumlanski <
>> jason at floridasolardesigngroup.com> wrote:
>>
>>> I'm seeing a lot of pictures of LiPO battery systems and people are
>>> mounting equipment above them like load centers, inverters with
>>> disconnects, and other serviceable enclosures. Some of these battery
>>> systems are 24 inches deep or more. This seems to violate NEC 110.26
>>> requirements for the other serviceable equipment, but the pictures are
>>> proudly displayed as models of success. Even slender Tesla Powerwalls stick
>>> out significantly when stacked 2 or 3 deep and would be more than 6 inches
>>> deeper than a standard load center. Sure, the battery cabinets make great
>>> places to rest tools while working, but does anyone else see this as
>>> problematic?
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210131/35e16fa6/attachment.htm>


More information about the RE-Wrenches mailing list