Hi Mac,

Yes, I considered using a pilot relay - it makes sense to run it on 120V
because relays are readily available. I had the exact same concern - more
to fail.

In this scenario, the inverter/battery room is remote from the house so
there is only one load I can switch easily with a contactor, and that's the
whole house load. Otherwise, I would definitely consider switching
non-critical loads in a low battery situation.

It just seems prudent enough to use the integrated Battery
Preservation Mode (BPM), even in this AC coupled system. I considered a
small DC array to charge the batteries in a heavily depleted situation, but
it's a 60kWh battery so I would need a pretty substantial "backup" array I
think. It does not seem like a reasonable solution. I would expect BPM to
do it's job and keep the batteries from reaching a state that they are not
recovered quite easily.

Jason



On Thu, Jan 21, 2021 at 2:37 PM Mac Lewis <maclewis1 at gmail.com> wrote:

> Hi Jason,
>
> The only reason to load shed, without using the internal preservation mode
> is if you have certain loads you'd like to keep on longer than other loads
> that you shed.  The various preservation modes can be complex, especially
> if you are AC coupled, so you really have to think through your strategy.
>
> You can always use a pilot relay, with a coil rating that suits your
> needs, and then feed the 100A contactor with that.  Unfortunately, its just
> one more piece to fail...
>
> On Thu, Jan 21, 2021 at 12:13 PM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
>
>> I just learned from the manufacturer that the mercury displacement
>> relay's coil is rated for 43.2 to 52.80V. Obviously, the battery voltage
>> can exceed 52.8 pretty significantly. Does the Sunny Island regulate the
>> output voltage on this relay to 48V or is the actual battery voltage passed
>> through on this terminal?
>>
>> The more I read about this load shedding strategy, the more it seems
>> overly complicated. It's also another thing to fail. If the N.O. contactor
>> coil fails, the loads to the house are going to lose power. That's not good
>> for a remote installation. I guess you have to weigh battery protection
>> with how critical the loads are.
>>
>> I'm wondering why the internal Battery Preservation Mode isn't sufficient
>> enough. What's the purpose of load shedding if the BPM does effectively the
>> same thing. I can see perhaps shedding some parts of the load and that is a
>> nice feature, but to protect the batteries, why isn't BPM enough?
>>
>> Jason
>>
>>
>>
>>
>> On Tue, Jan 19, 2021 at 8:48 PM Mac Lewis <maclewis1 at gmail.com> wrote:
>>
>>> Hi Jason,
>>>
>>> I have done this with mercury displacement relays:
>>>
>>> https://www.mdius.com/mercury-relays/two-pole-relays-contactors/two-pole-100-amp
>>> <https://mailtrack.io/trace/link/ff30c111d75d78887f17a5ed3e3b04bfe2cd428a?url=https%3A%2F%2Fwww.mdius.com%2Fmercury-relays%2Ftwo-pole-relays-contactors%2Ftwo-pole-100-amp&userId=1613865&signature=0abdef13355136e0>
>>>
>>> They do have a 100A 2P 48V coil relay.  They seem to work perfectly.
>>>
>>> Good luck
>>>
>>> On Tue, Jan 19, 2021 at 2:51 PM Jason Szumlanski <
>>> jason at floridasolardesigngroup.com> wrote:
>>>
>>>> Does anyone know where I can get a load shedding contactor described in
>>>> SMA documentation for use with a multi-function relay in a Sunny Island?
>>>>
>>>> Thanks,
>>>>
>>>> Jason Szumlanski
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/dc696cbe05b3c1c168fc9a22231ca0ead130049f?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=faa967f05b00e2a4>
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> <https://mailtrack.io/trace/link/160c10c9d1db65c3677175394dcc82fd4994efb3?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=e6df768a86360ef9>
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/e56aa4628cb2ce3c7cb2b56993deb964cf21012c?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=82b323bc4adc6a40>
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/d5e01cc24c09f7745d332a8e1b57dba7b65f9aee?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=91cd08f0bcb7f27a>
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/f61527617210dd511f7bf80a4a817b37be5349ac?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=cdc9edc7867187b4>
>>>>
>>>>
>>>
>>> --
>>>
>>>
>>>
>>> Mac Lewis
>>>
>>> *"Yo solo sé que no sé nada." -Sócrates*
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/539b4f46a78d0109f4b18fd8630c7324db4e85dc?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e37702430e2fa01d>
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> <https://mailtrack.io/trace/link/010fc687ef19380ff93d7c8e33ba37c51e868835?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=1fe5ea5f743578cf>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/4a62873ea528dfd6279d40b4347ab135d978da0c?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=08a4b1968d8723cd>
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/3e73673eede6e17016189c4ae611b9bc68766b10?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=57673f104a16c1bb>
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/3fd7a925b985577442cdb6c19e47cce4b15cc8a5?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4230b4333ecdbe88>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/9efe98433ffd8b15b133ae12f11579e25a0c5f7d?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=a2070240f48e4ccf>
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://mailtrack.io/trace/link/f0b2953fc2e2630da5f304cb44e90bdfb32d93de?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=6c80a029a0970e7e>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/0c2947de39c88364a737c43aa2eeb5b7b60e9ba1?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2e0f01c92f331eef>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/7eea73c333b4b1496ba4173a357d711ed6d8fda1?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8f4d40ddde72ea63>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/9a7989fa0af5dcd90b532c4b8acc96baaba230d9?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=a76d182f82c70658>
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/aa2fcefaf3aff99d20a6fe0b7344b278a45637fe?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=7dade94405b95707>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/trace/link/eedcc485a065928fafd0386d872a689b438c77a3?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=de33c0fc0f7b4919>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/468705b8b99ca36fc78ee90c0d2c818320af4ec8?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=429e74d774977536>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/6e89bc0d891a7cd6e22a33e9bf939b8f9381f599?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=388e63c5f6530b0b>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/d5c56c34000b127fec9f79fe1f6f9c874fd5b0a9?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=937aae7888024221>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210121/4aaf7d9d/attachment.htm>


More information about the RE-Wrenches mailing list