[RE-wrenches] Radian Charges 1 hour per calendar day
Steve Higgins
steve at surrette.com
Fri Jan 8 16:23:46 EST 2021
I don't know if this will help, but there is a setting under the AGS menus
called DC Generator.
There is DC Absrob timer and DC Absrob Votlage.
It's imperative that this is left alone if you are using an AC source, I
find many systems that are doing this the customer or installer freaked out
because the DC Genset Voltage is set at the default of 76 volts.
Make sure that this setting is back to 76 volts and left alone if you are
using an AC Generator.
Even if this is set to No and you have the voltage set too low it will mess
with your absorb timers.
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020 m +1.206.790.5840
f +1.902.597.8447 e steve at surrette.com
<#SignatureSanitizer_SafeHtmlFilter_> <http://www.facebook.com/RollsBattery>
<http://www.facebook.com/RollsBattery> <http://www.twitter.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
------------------------------
*Become a Certified PV Professional. Register for* *NABCEP CEC 2020*
<http://rollsbattery.com/nabcep2020> *using promo code* *20RBE*
<http://rollsbattery.com/nabcep2020>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------
On Fri, Jan 8, 2021 at 1:17 PM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:
> Same page with you Jay, as usual...
>
> Does the battery system go to absorb with solar still even if it is
> cloudy? Maybe a bad battery? Tis the season!
> Can the user go thru the set-points and make sure nothing has changed? Gen
> sets can do weird surges that can corrupt settings.
>
> If he has to leave, shut down the inverter? Is that an option? It is only
> a week right.
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsola
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> On Fri, 8 Jan 2021 13:39:40 -0700, Jay <jay.peltz at gmail.com> wrote:
> > Is it ags start and is it starting on volts or %, or load?
> >
> >
> >> On Jan 8, 2021, at 1:10 PM, Dave Angelini Offgrid Solar
> >> <offgridsolar at sti.net> wrote:
> >>
> >> You said both, it will go into absorb for an hour only and it will net
> >> go
> >> into absorb. Which one please?
> >>
> >> Is there an AGS?
> >>
> >>
> >> Dave Angelini Offgrid Solar
> >> "we go where powerlines don't"
> >> http://members.sti.net/offgridsolar/
> >> e-mail offgridsolar at sti.net
> >> text 209 813 0060
> >>
> >>> On Fri, 08 Jan 2021 13:33:56 -0500,
> drake.chamberlin at redwoodalliance.org
> >>> wrote:
> >>> Hello Wrenches,
> >>>
> >>> An off grid, Radian / Mate 3 system we set up some years back has
> worked
> >>
> >>> flawlessly. The client is now reporting that his system will only go
> >>> into absorption charge for 1 hour per calendar day. The setting was
> >>> previously to absorb for 2 hours.
> >>>
> >>> He has tried shutting off the generator and then restarting. The
> >>> inverter will connect, but not go into absorb.
> >>>
> >>> During this cloudy period, he is only able to get the batteries to
> about
> >>
> >>> 80 percent before he needs to leave the site for a week or so.
> >>>
> >>> I finally go through to Outback, and they think it is a Firmware
> >>> problem. As it is a long drive out, it seems worth while to run it by
> >>> the list. Does FW this seem like the issue?
> >>>
> >>> Thank you,
> >>>
> >>> Drake
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> There are two list archives for searching. When one doesn't work, try
> >> the other:
> >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> http://www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> http://www.members.re-wrenches.org
> >>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210108/36ac2c1d/attachment.htm>
More information about the RE-Wrenches
mailing list