[RE-wrenches] Remote Alert and Bootstrapping on Sunny Island AC Coupled System-Follow up
William Miller
william at millersolar.com
Sat Dec 19 02:19:31 EST 2020
Wrenches:
I found some time to review the .evt and .log files from the primary Sunny
Island inverter.
Prior to 12/8/20 the system was running normally with a generator run
averaging 6 hours about every other day.
On 12/8 at 06:00 the system tried to start the generator. There was no
indication the generator delivered voltage to the system. The system tried
to start the generator 168 times between 12/18 at 06:00 and 12/13 at
15:00. 168 times the system closed relay 1 and then opened it about 2
minutes later. Maybe the generator ran, maybe it didn’t, but no voltage
was delivered. On 12/15 the client started the generator and it produced
voltage into the inverter system. On 12/18 I started the generator and it
produced voltage.
Why this generator start cycle kept recurring is a mystery to me. There
may be a setting within the bowels of the menu system that I have
overlooked that limits the start attempts and I will be investigating
that. To me, navigating the Sunny Island menu system is like trying to
remember the DOS command-line interface. I need something much more
ergonomic.
Thanks for all of your priceless knowledge. I feel like we are a little
nerd family.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985