My memory is that you need to disconnect the Sunny Island from all AC and
DC voltages for 15-20 minutes before the low voltage lockout releases (I
think there is a small LED light on the internal circuit board which turns
off). Once that happens, you can reconnect the batteries and even with
fairly low voltage the SIs will boot up at which point the generator can
sync up and start charging the batteries. Just make sure to run the gennie
for a bit before you try this to warm it up, and set the connection time of
the inverters to the generator to be as short as possible so theSI's don't
shut off on Low Voltage before they do connect.
As far as the Sunny Portal, I too haven't messed with it for a few years
and SMA had just done a major overhaul of the sites capabilities, so I
didn't really explore it. And it probably now has more capability than
that upgrade afforded.
Howie
*Howie Michaelson**Sun Catcher*
*NABCEP Certified Solar PV Installerâ„¢*
*Solar Electric Systems Sales & Service802-272-0004*
On Thu, Dec 17, 2020 at 4:59 PM August Goers <august at luminalt.com> wrote:
> We had one Sunny Island system go totally dead years ago. The only way to
> get it running again was to charge the batteries, which we did in groups of
> two (6 volt batteries each) with a heavy duty 12 VDC automotive charger. It
> took about a week to charge all the batteries. Jerry, it's good to know
> that there are 48 VDC chargers out there. Do you have a model you like?
>
> William, once the battery bank voltage goes really low (I can't recall the
> cutoff voltage) the Sunny Island displays indeed turn completely off.
>
> We stopped installing Sunny Islands about 3 or 4 years ago. It is a solid
> product, but definitely part of the older generation of battery inverters
> that take a lot of skill to install and program properly to set the project
> up for success. The Sunny Portal at the time could give the owner a little
> insight into their battery state of charge, but I don't think it sends push
> notifications in real time. I think it will send error event notifications
> but they are delayed. You might check with SMA about the potential there.
>
> August
>
>
> On Thu, Dec 17, 2020 at 12:12 PM Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
>> Wrenches
>> This is why AC coupling is not the best solution but
>> you can program the SI to protect low voltage so if this happens you
>> still have headroom to reboot the system, also program the GT inverters not
>> to wait 300 sec to start. I would also suggest having a 48 vdc charger
>> wired directly to the gen set as a fail safe charger to wake up everything.
>> Jerry
>>
>> On Thu, Dec 17, 2020, 11:55 AM William Miller <william at millersolar.com>
>> wrote:
>>
>>> Friends:
>>>
>>>
>>>
>>> I have a client living off-grid with a Sunny Island system AC coupled to
>>> Sunny Boy inverters. They returned from being away to find the system
>>> entirely shutdown due to cloudy weather, a dead generator cranking battery
>>> and a water leak which ran two booster pumps continuously over a period of
>>> time. The displays on the Sunny Islands were blank and therefore the
>>> inverters would not start.
>>>
>>>
>>>
>>> We put a new cranking battery into the generator and got it started, but
>>> with no life in the Sunny Islands, neither the generator nor the Sunny Boys
>>> had any possibility of reviving the discharged 6,000 amp-hour lead acid
>>> battery array. Fortunately after disconnecting the batteries for ten
>>> minutes, the voltage rebounded just enough to start the Sunny Islands which
>>> allowed the generator to connect and we were back in operation.
>>>
>>>
>>>
>>> I am not sure why the displays went dead on the Sunny Islands. I am on
>>> my way back out to download and examine the SD card logs. I have developed
>>> an Excel tool to help me tabulate the data. Maybe there is some clue in
>>> those files.
>>>
>>>
>>>
>>> In the meantime I have these questions that those of you with more Sunny
>>> Island experience might be able to answer:
>>>
>>>
>>>
>>> 1. Is it normal for the display screens on the Sunny Islands to go
>>> blank after shutting off due to low battery voltage?
>>>
>>>
>>>
>>> 2. Is there an up-to-date option for remote monitoring that will send
>>> an email if certain error conditions occur?
>>>
>>>
>>>
>>> 3. What would you do with a 6k AH battery bank with a voltage too low
>>> to start a battery inverter or solar charge controller?
>>>
>>>
>>>
>>> Thanks in advance. The wrenches hive-mind is a huge asset.
>>>
>>>
>>>
>>> William Miller
>>>
>>> Miller Solar
>>>
>>> 17395 Oak Road, Atascadero, CA 93422
>>>
>>> 805-438-5600
>>>
>>> www.millersolar.com
>>>
>>> CA Lic. 773985
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201217/49650286/attachment.htm>
More information about the RE-Wrenches
mailing list