[RE-wrenches] Conext SW4048 not charging from generator

Chris Sparadeo sparadeo.chris at gmail.com
Tue Dec 15 14:32:30 EST 2020


Try having them decreasing the Max Charge Rate to 50% and monitoring the AC
output, specifically looking for spikes and dips in voltage and frequency
via the SCP. Although you can open AC input parameters to allow for dirtier
power to be qualified, I would definitely suggest against this. Sounds like
they need a higher quality generator. Keep in mind that the SW 4048 is a
45A max DC charger.

On Tue, Dec 15, 2020 at 2:21 PM Ray <ray at solarray.com> wrote:

> Definitely the generator.  Harbor Freight?  4 kW into a 4 kW charger?
> What's the altitude?   I believe that 4 kW generator is actually only 3.5
> kW continuous rated.   By the time you derate for altitude, and then
> account for the generator not being built to be a prime power unit, its
> probably reasonable to derate it 50%.  Then yet another thing,  those
> gennies are 240/120 so you only get half the rated power at 120 vac, and it
> unbalances the load on the generator.  Is that Conext 240/ 120 or just
> 120vac ?
>
> Its just going to be a head ache for everyone until they buy something
> much better.  They really need something in the 6.5 kW to 9 kW range, and
> 240 to 120 transformer if the Conext is not the 240/120 model, so that the
> generator is loaded evenly.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 12/15/20 1:57 PM, Sindelar Solar wrote:
>
> Dave,
>
> I would first suspect the generator, not the inverter. Check its output
> voltage and Hz under load. If it's overloading, either (or both) voltage
> and frequency will drop below the acceptable range and the inverter will
> unlatch its input relays, wait for a bit, relatch and ramp up input amps
> until it again overloads and the cycle repeats. You may reduce either (or
> both) charging amps and overall input amps, broaden the frequency and
> minimum voltage acceptance ranges (I don't recommend this), adjust the AC
> output voltage of the generator, or advise them to get a better gennie.
>
> Allan
> On 12/15/2020 11:14 AM, Dave Tedeyan wrote:
>
> Hi All,
>
> I am going to service a system where the homeowner is telling me that
> their Conext SW4048 had been working fine for 14 months, and then all of a
> sudden recently stopped being able to charge the batteries from the
> generator. It is an off grid system.
>
> The inverter would start charging the batteries, but then about a minute
> later they would hear a relay click and the charging would stop. Then it
> would just keep cycling. If they turned everything off for a while, they
> could then turn it back on and charge for maybe 10 minutes before it would
> start cycling. They just have a crappy 4kw generator from Harbor Freight.
>
> I have not laid my own eyes on it yet, but will be there in the next day
> or two. Just wondering if anyone has experienced these symptoms and have a
> good idea of what to look for first.
>
> Thanks!
> -Dave
>
> *Dave Tedeyan, PE*
> Senior Engineer | Taitem Engineering, PC
>
> 110 South Albany Street
> <https://www.google.com/maps/search/110+South%0D%0A++++++++++++++++++++++++++++++++++++++++++++++Albany+Street+%C2%A0%7C+Ithaca,+NY+14850?entry=gmail&source=g> |
> Ithaca, NY 14850
> <https://www.google.com/maps/search/110+South%0D%0A++++++++++++++++++++++++++++++++++++++++++++++Albany+Street+%C2%A0%7C+Ithaca,+NY+14850?entry=gmail&source=g>
> o. *607.277.1118 x121*  f. 607.277.2119
> www.taitem.com
>
> Solar • Sustainability • Energy • Design
> Certified B-Corporation since 2013
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:http://www.members.re-wrenches.org
>
> --
>
> *Allan Sindelar*
> allan at sindelarsolar.com
> NABCEP Certified PV Installation Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> *505 780-2738 cell*
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo


C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201215/0a7d33a8/attachment.htm>


More information about the RE-Wrenches mailing list