[RE-wrenches] Outback AC Backfeed Error
William Miller
william at millersolar.com
Fri Dec 11 21:03:43 EST 2020
Jon:
In the deep recess of my memory I recall this error code with FX
inverters. It was caused by a stuck transfer relay. You might open the
inverter cover and look for signs of smoke or arcing in the relay.
Good luck!
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Jon Siegenthaler
*Sent:* Friday, December 11, 2020 6:01 PM
*To:* re-wrenches at lists.re-wrenches.org
*Subject:* [RE-wrenches] Outback AC Backfeed Error
Hey wrenches,
I have a client who has a couple of the Radian 8048's and has an error code
of "AC Backfeed Error GS-1". Looking at the manual it states that "Usually
indicates another AC power source (out of phase with the inverter) was
connected to the unit’s AC output. Can also occur if an out-of-phase AC
source is connected to the inverter’s AC input."
However when this happened the generator wasn't running and it's an off
grid system. Is there a way that the master is looking to the slave as
another power source? The system had been running fine this week, auto
running the generator early morning and shutting down on its own.
Anyone seen something like this before? Thanks,
Jon Siegenthaler