[RE-wrenches] Enphase intermittent breaker trippjng

Chris Worcester chris at solarwindworks.com
Thu Nov 19 13:27:07 EST 2020


Hi Jason,I don't know if this has been suggested yet, when we have electrical equipment in exterior and damp locations we're a firm believer in putting no-ox or electrical grease on all electrical connections, coating fuse ends and contact points, disco conductor terminal points, CB wire lands, CBs on the buss, ground conductor to ground buss, etc. This has been saving me from a lot of grief when it comes to resistance and corrosion forming in connections, splices, contact locations. Probably leftover from early on learning that  coating and assembling battery lugs and cable ends with high temperature lithium grease works well to keep the oxygen off and stop oxidation. Chris Worcester chris at solarwindworks.com530-448-9692Sent from my Samsung Galaxy s9.
-------- Original message --------From: Jason Szumlanski <jason at floridasolardesigngroup.com> Date: 11/19/20  7:15 AM  (GMT-08:00) To: RE-wrenches <re-wrenches at lists.re-wrenches.org> Subject: Re: [RE-wrenches] Enphase intermittent breaker trippjng All good info.I plan to take my FLIR One out next time. I can paint it white in both cases I suppose. As for the temps, the high ambient here is 93ºF per ASHRAE. Inside attics, we can see temps exceeding 140ºF here. We don't derate conductors for that. I'm not sure where 114ºF comes from, but I get the point. The interior of the enclosure can certainly get blazing hot. This definitely seems to be a heat-related issue whether the NEC intent has been met or not. Upping the tap conductors to #4 or larger would not be difficult or expensive to accomplish. I will likely make that our new standard for 50A and 60A calculated circuits for supply-side interconnections made outdoors.JasonOn Wed, Nov 18, 2020 at 8:13 PM Ray <ray at solarray.com> wrote:
  
    
  
  
    What is the brand and model of the disconnect? Temp ratings of
      the terminals?  I've definitely had fuse holders not make good
      contact with the fuses and burn the fuses at one end, instead of
      in the middle.  Have you looked at it with a Thermal imaging
      camera when its operating to see if its hot on one end of the
      fuse?  
    
    Second, depending on the temperature it would be hitting inside
      the enclosure in the sun, you could be exceeding the rating of the
      #6 conductor.  Assuming terminals rated at 75C, then from 310.16,
      a #6 is rated 65 A, but derate for temperature of 114F inside the
      enclosure gets you to .82 x 65 = 53.3, which is a bit less than
      the 54.45 that Dave just calculated for continuous duty.  
    
    What color is the disconnect painted?  any chance of painting it
      white?
    
    Ray Walters
Remote Solar
303 505-8760
    On 11/18/20 4:16 PM, Dave Tedeyan
      wrote:
    
    
      
      Jason, 
        Bright sunny days, disconnect on the west side of house,
          maybe in the sun? 43.56A * 1.25 for continuous duty = 54.45A.
          If these disconnects are also baking in the sun, maybe the
          extra ambient heat is enough to push it over the edge? Just a
          thought.
        Cheers,
        Dave
          
            
              
                
                  
                    
                      
                        
                          
                            
                              
                                
                                  
                                    
                                      
                                        
                                        
                                        Dave Tedeyan,
                                              PE
                                        Senior Engineer
                                            | Taitem Engineering, PC
                                        
                                          
                                        110 South Albany
                                            Street |
                                            Ithaca, NY 14850
                                        o. 607.277.1118
                                              x121  f. 607.277.2119
                                        www.taitem.com
                                        
                                        
                                        Solar • Sustainability • Energy • Design
                                        
                                        Certified
                                              B-Corporation since 2013
                                            
                                      
                                    
                                  
                                
                              
                            
                          
                        
                      
                    
                  
                
              
            
          
          
        
      
      
      
        On Wed, Nov 18, 2020 at 3:41
          PM Jay <jay.peltz at gmail.com> wrote:
        
        
          
            Hi Jason
            
            
            Any chance for some photos?
            
            
            Jay
            
              On Nov 18, 2020, at 12:18 PM,
                Jason Szumlanski <jason at floridasolardesigngroup.com>
                wrote:
                
              
            
            
              
                
                  
                    The
                      plot thickens on the fuse blowing issue. Again, we
                      tore the Enphase IQ system apart looking for any
                      reason for the fuse to keep blowing. We
                      reconfirmed torque on all line side conductors to
                      the service (supply side interconnection using
                      Polaris taps).
                    
                    
                    Low
                      and behold, I get a second client with the exact
                      same issue yesterday. The circumstances are
                      eerily alike. Both disconnects are located on the
                      west side of the house and have 36 IQ7+
                      microinverters on an IQ Combiner, requiring 60A
                      fuses on the 60A fusible disconnect. The combined
                      inverter output rating is 43.56A. The
                      interconnections are identical with #6 THHN 90ºC
                      conductors and Polaris taps. Both disconnects have
                      conductors on the right-hand side line-side
                      terminal that are discolored (the copper is
                      silvery, the insulation is not burned). The fuses
                      blow at peak current around 1:30 pm, only on
                      bright and sunny days.
                    
                    
                    I'm
                      starting to suspect a faulty fusible disconnect
                      switch. Maybe the blades are not making proper
                      contact with the line side terminals.
                    
                    
                    For
                      the client who is having regular/frequent fuses
                      blowing I plan to replace the disconnect with a
                      heavy-duty version or possibly get a 100A
                      disconnect with fuse reducers. I'm not sure which
                      option would yield a better test. I might also
                      switch brands.
                    
                    
                    Currently,
                      we are using GE TG3222R. The fuses are Bussman
                      FRN-R Time Delay. I have to believe a heavy-duty
                      switch would be less susceptible to this, but
                      maybe a higher rated one would be a better option.
                      I'm not a fan of fuse reducers, however. 
                    
                    
                    Jason
                      Szumlanski
                    Florida
                      Solar Design Group
                    
                    
                  
                  
                  
                    On Sun, Aug 30,
                      2020 at 5:54 PM Jason Szumlanski <jason at floridasolardesigngroup.com>
                      wrote:
                    
                    
                      
                        
                          The
                            tripping breaker occurred at random times,
                            even at night. No weather-related
                            correlation.
                          
                          
                          I
                            have more research to do to see when this
                            fuse issue is happening, but previous visits
                            showed no water ingress. I'm not sure about
                            temperature.
                          
                          
                          
                            
                              
                                
                                  
                                    
                                      
                                        
                                          
                                              
                                              
                                            
                                        
                                      
                                    
                                  
                                
                              
                            
                          
                          
                        
                        
                        
                          On Thu, Aug
                            27, 2020 at 8:51 PM Jay <jay.peltz at gmail.com>
                            wrote:
                          
                          
                            
                              Hi Jason
                              
                              
                              One thought I have about
                                the blowing fuse is to check it with a
                                IR tool. 
                              
                              
                              I suspect a poor connection
                                of the fuse to holder which during
                                higher air temp is causing it to fail.  
                              I’m assuming that the
                                correct amp size and slow blow fuse Is
                                installed and that the wire connections
                                are done correctly. But again an IR tool
                                during peak heat would be  a good test. 
                              
                              
                              About the enphase fix, wow
                                what a head scratcher. But given that
                                it’s fixed it means that it’s not a
                                short, but enough amps going through
                                over enough time to trip it. I wonder if
                                a magnetic hydraulic vs thermal breaker
                                ( CBI  vs CH etc) would have worked?
                              
                              
                              Is that breaker box ever in
                                the sun?  Is there any Correlation
                                between  high ambient temperatures and
                                tripping?  
                              
                              
                              It sure would keep me up at
                                night too 
                              
                              
                              Jay
                              
                              
                              
                                On Aug 27, 2020,
                                  at 4:29 PM, Jason Szumlanski <jason at floridasolardesigngroup.com>
                                  wrote:
                                  
                                
                              
                              
                                
                                  
                                    So the resolution to this is
                                      in... But I still have no idea
                                      what was wrong. 
                                    
                                    
                                    The string of 10
                                      offending microinverters was split
                                      into 5 and 5. We had a spare
                                      breaker in the IQ Combiner so it
                                      was relatively easy to run another
                                      branch circuit. It has been over
                                      two months with no recurrence. So
                                      the issue seems to be resolved,
                                      but again, no idea why.
                                    
                                    
                                    So here we go
                                      again... On another system we have
                                      a similar problem now. In this
                                      case it is supply side
                                      interconnected with a fusible
                                      disconnect. The same fuse (same
                                      line) keeps blowing every few to
                                      several weeks. We can't find any
                                      home run wiring issues or issues
                                      with terminator caps. There are no
                                      apparent faults in the AC
                                      Combiner. We have no idea why
                                      this is happening. But in this
                                      system, just the fuse blows, not
                                      one of the individual branch
                                      circuit breakers. 
                                    
                                    
                                    This is getting very
                                      frustrating. And this is way more
                                      serious because fuses and service
                                      calls are expensive and I can't
                                      isolate the issue to one branch
                                      circuit. I don't even know where
                                      to start. Leaving each circuit
                                      disconnected for several weeks to
                                      prove a negative is an untenable
                                      suggestion to make to a client.
                                      But I don't see any other good
                                      options. 
                                    
                                    
                                    Jason Szumlanski 
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                    
                                      
                                      
                                        On Tue, Jun
                                          9, 2020, 3:42 PM Jason
                                          Szumlanski <jason at floridasolardesigngroup.com>
                                          wrote:
                                        
                                        
                                          
                                            
                                              Yes,
                                                we double-checked that.
                                                I have seen that happen
                                                before and it's one of
                                                my early diagnostic
                                                steps for something like
                                                this.
                                              
                                              
                                              
                                                
                                                  
                                                    
                                                      
                                                        
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                        
                                                      
                                                    
                                                  
                                                
                                              
                                              
                                            
                                            
                                            
                                              On
                                                Tue, Jun 9, 2020 at 9:18
                                                AM Mac Lewis <maclewis1 at gmail.com>
                                                wrote:
                                              
                                              
                                                Hi Jason,
                                                  
                                                  
                                                  Are you certain
                                                    that the branch
                                                    circuits aren't
                                                    crisscrossed
                                                    somewhere, meaning
                                                    that an L1 branch 1,
                                                    isn't connected to
                                                    an L2 branch 2? 
                                                    That could explain
                                                    two different
                                                    breakers tripping.  
                                                  
                                                  
                                                  Good luck
                                                  
                                                  
                                                
                                                
                                                
                                                  On
                                                    Wed, Jun 3, 2020 at
                                                    1:07 PM Jason
                                                    Szumlanski <jason at floridasolardesigngroup.com>
                                                    wrote:
                                                  
                                                  
                                                    
                                                      
                                                        Undoubtedly,
                                                          the
                                                          termination
                                                          caps are the
                                                          second thing
                                                          we check after
                                                          the rooftop
                                                          junction box(es).
                                                          These are
                                                          prone to
                                                          installation
                                                          errors, even
                                                          when the right
                                                          parts are
                                                          used. And
                                                          given the
                                                          cost, I've
                                                          thought very
                                                          long and hard
                                                          about
                                                          abandoning
                                                          them
                                                          altogether and
                                                          terminating
                                                          strings in
                                                          small j-boxes
                                                          with
                                                          watertight
                                                          fittings. But
                                                          in this case,
                                                          there was no
                                                          evidence of
                                                          improper
                                                          installation
                                                          (we replaced
                                                          them) and it
                                                          was not
                                                          correlated to
                                                          rain events.
                                                        
                                                        
                                                        We
                                                          are well
                                                          equipped with
                                                          bare Q-cable
                                                          and field
                                                          wireables that
                                                          we could use
                                                          for
                                                          troubleshooting
                                                          to bypass
                                                          certain
                                                          sections, but
                                                          the
                                                          intermittent
                                                          nature of the
                                                          problem and
                                                          unpredictable
                                                          timeframe
                                                          between faults
                                                          is very
                                                          frustrating.
                                                          While this is
                                                          a
                                                          rare occurrence,
                                                          it is
                                                          definitely a
                                                          "con" to
                                                          consider when
                                                          comparing
                                                          string vs.
                                                          microinverters
                                                          that I had not
                                                          strongly
                                                          considered in
                                                          the past. I'm
                                                          intent on
                                                          getting to the
                                                          bottom of this
                                                          in order to
                                                          learn what to
                                                          look for in
                                                          the future and
                                                          how to
                                                          approach
                                                          diagnoses of
                                                          Enphase
                                                          branch circuit faults.
                                                        
                                                        
                                                        Jason
                                                        
                                                        
                                                        
                                                        
                                                        
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                        
                                                        
                                                      
                                                      
                                                      
                                                        On
                                                          Wed, Jun 3,
                                                          2020 at 2:31
                                                          PM Amos Post
                                                          <integrityenergy101 at gmail.com>
                                                          wrote:
                                                        
                                                        
                                                          I was
                                                          just at a site
                                                          last week
                                                          where the
                                                          Enphase branch
                                                          circuit
                                                          breaker,
                                                          outside
                                                          utility
                                                          disconnect
                                                          breaker, and
                                                          feed breaker
                                                          in the main
                                                          panel all
                                                          tripped
                                                          simultaneously,
                                                          and it
                                                          happened about
                                                          1 hour before
                                                          I showed up
                                                          onsite.  The
                                                          customer said
                                                          it had
                                                          happened 1
                                                          other time
                                                          last fall but
                                                          that time it
                                                          was just the 1
                                                          branch circuit
                                                          in the Enphase
                                                          combiner
                                                          panel. 
                                                          Interestingly
                                                          the customer
                                                          mentioned that
                                                          he had just
                                                          washed off the
                                                          panels, also
                                                          about 1 hour
                                                          before I got
                                                          there.  I went
                                                          on the roof
                                                          and found that
                                                          the installing
                                                          contractor had
                                                          not put on the
                                                          Enphase
                                                          termination
                                                          caps.  1
                                                          string was
                                                          wire-nutted
                                                          with regular
                                                          wire nuts and
                                                          sitting on the
                                                          roof, and the
                                                          roof was damp
                                                          right there.
                                                          This was a
                                                          fairly flat
                                                          roof.  The
                                                          other micro
                                                          trunk cable
                                                          was just cut
                                                          with no
                                                          protection at
                                                          all, tied to
                                                          the rail…
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          <IE
                                                          LOGO
                                                          150x78.jpg>
                                                          
                                                          
                                                           
                                                               Amos Post
                                                           
                                                           Integrity
                                                          Energy
                                                           
                                                          W 802.763.7023
                                                           
                                                           C
                                                          802.291.2188
                                                           
                                                            ienergyVT.com
                                                           
                                                                Facebook
                                                          
                                                          
                                                          
                                                          On Jun 3,
                                                          2020, at 2:05
                                                          PM, Jason
                                                          Szumlanski
                                                          <jason at floridasolardesigngroup.com>
                                                          wrote:
                                                          
                                                          
                                                          
                                                          
                                                          The
                                                          breaker in the
                                                          main panel IS
                                                          tripping
                                                          simultaneously
                                                          with one of
                                                          the branch
                                                          circuit
                                                          breakers each
                                                          time.
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          On Wed, Jun 3, 2020 at 12:43 PM Jay <jay.peltz at gmail.com>
                                                          wrote:
                                                          
                                                          
                                                          
                                                          A
                                                          question that
                                                          keeps nagging
                                                          me is why do
                                                          these breakers
                                                          trip and not
                                                          the breaker in
                                                          the main
                                                          panel?  
                                                          Presuming
                                                          there is a 40
                                                          amp in the
                                                          main
                                                          
                                                          
                                                          I
                                                          would have
                                                          thought that
                                                          given all the
                                                          times the
                                                          breakers have
                                                          tripped at
                                                          some point
                                                          that one would
                                                          have tripped
                                                          and I can’t
                                                          understand why
                                                          not?  
                                                          
                                                          
                                                          Jay 
                                                          
                                                          On
                                                          Jun 3, 2020,
                                                          at 8:27 AM,
                                                          Jerry Shafer
                                                          <jerrysgarage01 at gmail.com>
                                                          wrote:
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          Wrenches
                                                          Looking
                                                          g at the
                                                          bigger breaker
                                                          tripping at
                                                          the same time
                                                          is very likely
                                                          do to response
                                                          time of the
                                                          breaker
                                                          nothing more.
                                                          As l suggested
                                                          in a previous
                                                          message. Use a
                                                          non bridged
                                                          breaker to see
                                                          if it is one
                                                          or both legs
                                                          that trip.
                                                          Also an eguage
                                                          will help to
                                                          see what if
                                                          anything leads
                                                          up to the
                                                          failure and
                                                          when. 
                                                          Jerry
                                                          Jerry
                                                          
                                                          
                                                          
                                                          On Wed, Jun 3, 2020, 7:58 AM Jason Szumlanski <jason at floridasolardesigngroup.com> wrote:
                                                          
                                                          
                                                          
                                                          
                                                          I
                                                          wonder about
                                                          that. Of
                                                          course, it
                                                          could be the
                                                          "inverter
                                                          output
                                                          circuit"
                                                          having a fault
                                                          in the wiring
                                                          still (an
                                                          intermittent
                                                          issue
                                                          somewhere
                                                          within the IQ
                                                          cable or home
                                                          run wiring).
                                                          But internal
                                                          to the
                                                          microinverter,
                                                          is it possible
                                                          that a fault
                                                          could still
                                                          occur at
                                                          night? I had a
                                                          suggestion
                                                          from another
                                                          wrench that
                                                          there are film
                                                          capacitors on
                                                          the AC output
                                                          side, but are
                                                          these isolated
                                                          when there is
                                                          no DC input?
                                                          It seems
                                                          unlikely that
                                                          this would be
                                                          an issue, but
                                                          I have seen
                                                          microinverters
                                                          reporting a
                                                          couple of
                                                          watts at night
                                                          (in
                                                          Enlighten).
                                                          I'm not sure
                                                          how real that
                                                          is.
                                                          
                                                          
                                                          The
                                                          overriding
                                                          question I
                                                          have is what
                                                          kind of fault
                                                          would cause
                                                          BOTH a branch
                                                          circuit and
                                                          the main solar
                                                          breaker to
                                                          trip
                                                          simultaneously?
                                                          That seems odd
                                                          to me. If any
                                                          normal load
                                                          branch circuit
                                                          has a fault,
                                                          you don't
                                                          often see
                                                          premises main
                                                          breakers
                                                          tripping, or
                                                          even feeder
                                                          circuit
                                                          breakers.
                                                          
                                                          
                                                          I
                                                          got to
                                                          thinking that
                                                          maybe there is
                                                          some kind of
                                                          issue between
                                                          the BR220 and
                                                          CH240 breakers
                                                          not playing
                                                          nicely
                                                          together. But
                                                          I would think
                                                          this would be
                                                          a well-known
                                                          issue because
                                                          I'm sure there
                                                          are tons of CH
                                                          feeder
                                                          breakers in
                                                          the wild with
                                                          BR branch
                                                          circuits
                                                          downstream. 
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          On Tue, Jun 2, 2020 at 9:25 AM <drake.chamberlin at redwoodalliance.org>
                                                          wrote:
                                                          
                                                          
                                                          
                                                          If it trips
                                                          at night, we
                                                          know it is not
                                                          the output
                                                          from the
                                                          inverters
                                                          causing the
                                                          tripping. The
                                                          current must
                                                          be coming from
                                                          the grid.
                                                          ---
                                                           
                                                          
                                                          
                                                          
                                                          On
                                                          2020-06-01
                                                          12:05, Jason
                                                          Szumlanski
                                                          wrote:
                                                          
                                                          
                                                          
                                                           
                                                          
                                                          It's
                                                          not weather.
                                                          It's at all
                                                          times of the
                                                          day and night,
                                                          and I
                                                          confirmed that
                                                          there is no
                                                          correlation to
                                                          rain or high
                                                          winds. That
                                                          was my first
                                                          suspicion.
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          On
                                                          Mon, Jun 1,
                                                          2020 at 10:27
                                                          AM Ray <ray at solarray.com> wrote:
                                                          
                                                          
                                                          Is it at
                                                          all weather
                                                          related? 
                                                          Rain, or high
                                                          humidity? 
                                                          High
                                                          temperatures? 
                                                          Do you have
                                                          any indication
                                                          what time of
                                                          day it trips
                                                          off at?
                                                          Ray Walters
Remote Solar
303 505-8760
                                                          On 6/1/20
                                                          10:23 AM,
                                                          Jason
                                                          Szumlanski
                                                          wrote:
                                                          
                                                          Well,
                                                          that didn't
                                                          resolve it.
                                                          The main
                                                          breaker and a
                                                          branch circuit
                                                          breaker
                                                          tripped again
                                                          a few days
                                                          ago. It was
                                                          the same
                                                          branch this
                                                          time. 
                                                           
                                                          As
                                                          my next
                                                          diagnostic
                                                          step I swapped
                                                          two circuits
                                                          (on which
                                                          breaker they
                                                          are landed).
                                                          If history is
                                                          a guide, it
                                                          will work for
                                                          about two
                                                          weeks and then
                                                          trip again.
                                                           
                                                          I'm
                                                          dumbfounded. I
                                                          really don't
                                                          want to have
                                                          to tear this
                                                          whole system
                                                          apart. At this
                                                          point, if I
                                                          have to remove
                                                          all the
                                                          modules, I
                                                          feel that I
                                                          need to
                                                          replace all of
                                                          the trunk
                                                          cable which is
                                                          an expensive
                                                          proposition. I
                                                          really don't
                                                          know what else
                                                          to do at this
                                                          point.
                                                           
                                                          Jason
                                                           
                                                          
                                                          
                                                          
                                                          On
                                                          Mon, May 25,
                                                          2020, 10:43 AM
                                                          Jason
                                                          Szumlanski
                                                          <jason at floridasolardesigngroup.com>
                                                          wrote:
                                                          
                                                          
                                                          
                                                          I
                                                          strongly
                                                          suspect the
                                                          CH240 combined
                                                          breaker was
                                                          compromised
                                                          (we will see).
                                                          Since it
                                                          happened that
                                                          two different
                                                          strings
                                                          tripped, I
                                                          doubt I have
                                                          two
                                                          microinverters
                                                          with internal
                                                          faults. It has
                                                          to be the
                                                          combined
                                                          breaker. I was
                                                          just surprised
                                                          that branch
                                                          circuit
                                                          breakers were
                                                          tripping
                                                          simultaneously with
                                                          the combined
                                                          output
                                                          breaker.
                                                           
                                                          Of
                                                          all the supply
                                                          side connected
                                                          systems I have
                                                          installed, I
                                                          have never
                                                          seen a
                                                          combined
                                                          output fusible
                                                          disconnect
                                                          fuse blow, but
                                                          I have seen
                                                          many combined
                                                          output
                                                          breakers
                                                          tripped. I was
                                                          worried early
                                                          on that I
                                                          would be
                                                          replacing
                                                          fuses
                                                          constantly,
                                                          but that has
                                                          not been an
                                                          issue
                                                          whatsoever.
                                                           
                                                           
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                           
                                                           
                                                          
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          On
                                                          Thu, May 21,
                                                          2020 at 11:15
                                                          AM <scot.arey at solarcentex.com>
                                                          wrote:
                                                          
                                                          
                                                          
                                                          Actually,
                                                          we had a IQ7
                                                          string loaded
                                                          up to its max
                                                          panel size and
                                                          max string
                                                          length and in
                                                          the spring on
                                                          cool, clear
                                                          day, it
                                                          tripped the
                                                          string's
                                                          associated
                                                          breaker in the
                                                          Enphase
                                                          combiner.
                                                           
                                                          
                                                          We reset
                                                          but of course
                                                          that breaker
                                                          was impaired
                                                          and it tripped
                                                          again. We
                                                          replaced and
                                                          never had an
                                                          issue going
                                                          forward. We
                                                          suspect the
                                                          breaker was
                                                          less than
                                                          perfect from
                                                          the start as
                                                          we've add
                                                          equally nice
                                                          days since.
                                                           
                                                          
                                                          This almost
                                                          reminds me of
                                                          loading up
                                                          Outback FM80.
                                                          It says 4,000
                                                          watts but in
                                                          reality, 3,600
                                                          is the max
                                                          when amps
                                                          spike. I will
                                                          be extra
                                                          careful going
                                                          forward on IQ7
                                                          string length
                                                          when going to
                                                          the max
                                                          published...
                                                           
                                                          
                                                          My story.
                                                           
                                                          
                                                          Scot
                                                           
                                                          
                                                          
                                                          From: RE-wrenches
                                                          <re-wrenches-bounces at lists.re-wrenches.org> On
                                                          Behalf Of Jason
                                                          Szumlanski
                                                          Sent: Thursday,
                                                          May 21, 2020
                                                          8:57 AM
                                                          To: RE-wrenches
                                                          <re-wrenches at lists.re-wrenches.org>
                                                          Subject: [RE-wrenches]
                                                          Enphase
                                                          intermittent
                                                          breaker
                                                          trippjng
                                                          
                                                           
                                                          
                                                          
                                                          I'm trying
                                                          to resolve an
                                                          intermittent
                                                          frustrating
                                                          problem with
                                                          and Enphase IQ
                                                          system. There
                                                          are three AC
                                                          Branch
                                                          circuits of 9
                                                          microinverters
                                                          each coming
                                                          into an
                                                          Enphase AC
                                                          combiner. 
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          What has
                                                          been happening
                                                          is one of the
                                                          BR220 branch
                                                          circuit
                                                          breakers and
                                                          the combine
                                                          CH240 breaker
                                                          in the main
                                                          backfed load
                                                          center have
                                                          been tripping
simultaneously. It has happened about four times in the last 6 months.
                                                          It was always
                                                          the same
                                                          branch circuit
                                                          breaker, so we
                                                          kept
                                                          investigating
                                                          that string,
                                                          checking the
                                                          junction box,
                                                          trunk cable,
                                                          and cap, etc.
                                                          Finally we
                                                          swapped out
                                                          the BR220
                                                          breaker. 
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          Fast
                                                          forward 4
                                                          weeks, and we
                                                          got another
                                                          call. This
                                                          time a
                                                          different
                                                          branch circuit
                                                          breaker and
                                                          the main
                                                          breaker
                                                          tripped
                                                          simultaneously.
                                                          We checked
                                                          that branch
                                                          circuit and
                                                          could not find
                                                          any fault. It
                                                          seems unlikely
                                                          that two
                                                          branch circuit
                                                          breakers would
                                                          be faulty, so
                                                          we have now
                                                          switched out
                                                          the CH240 main
                                                          breaker in
                                                          hopes that it
                                                          is the
                                                          culprit.  
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          I'm not
                                                          totally
                                                          confident in
                                                          this
                                                          resolution and
                                                          I have my
                                                          fingers
                                                          crossed. If
                                                          that doesn't
                                                          work, does
                                                          anyone have
                                                          any
                                                          suggestions on
                                                          another
                                                          diagnostic
                                                          step? These
                                                          intermittent
                                                          problems are a
                                                          major hassle.
                                                          One thought I
                                                          had was to
                                                          switch to a
                                                          supply side
                                                          interconnection
                                                          with a fusible
                                                          disconnect.
                                                          Maybe the
                                                          intermittent
                                                          fault would
                                                          blow one of
                                                          the two line
                                                          fuses so at
                                                          least I could
                                                          narrow it down
                                                          to which line
                                                          the fault is
                                                          on if there is
                                                          in fact a
                                                          fault.
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          I have
                                                          experienced
                                                          two other
                                                          tripping
                                                          breaker issues
                                                          with Enphase
                                                          systems in the
                                                          past. Neither
                                                          of them were
                                                          systems I
                                                          installed. One
                                                          turned out to
                                                          be branch
                                                          circuits that
                                                          were not
                                                          properly
                                                          paired up and
                                                          landed on
                                                          different
                                                          breakers.
                                                          Another time
                                                          we had an
                                                          inverter with
                                                          an internal
                                                          fault which
                                                          eventually"blew
                                                          up" with a
                                                          loud popping
                                                          noise and
                                                          smoke
                                                          billowing out
                                                          of it. That
                                                          happened after
                                                          resetting a
                                                          trip breaker
                                                          multiple
                                                          times. This
                                                          case seems to
                                                          be unrelated
                                                          to those
                                                          issues. I'm
                                                          perplexed. 
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          Jason
                                                          Szumlanski
                                                          
                                                          
                                                          Florida
                                                          Solar Design
                                                          Group
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                           
                                                          
                                                          
                                                          
                                                          
                                                          
_______________________________________________
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                          
                                                        
                                                      
                                                    
                                                  
                                                
                                                
                                              
                                            
                                            
                                        
                                      
                                    
                                  
                                  <IE LOGO 150x78.jpg>
                                  _______________________________________________
                                  List sponsored by Redwood
                                    Alliance
                                  
                                  List Address: RE-wrenches at lists.re-wrenches.org
                                  
                                  Change listserver email address
                                    & settings:
                                  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
                                  
                                  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
                                  
                                  List rules & etiquette:
                                  www.re-wrenches.org/etiquette.htm
                                  
                                  Check out or update participant
                                    bios:
                                  www.members.re-wrenches.org
                                  
                                
                              
                            
_______________________________________________
                            List sponsored by Redwood Alliance
                            
                            List Address: RE-wrenches at lists.re-wrenches.org
                            
                            Change listserver email address &
                            settings:
                            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
                            
                            List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
                            
                            List rules & etiquette:
                            www.re-wrenches.org/etiquette.htm
                            
                            Check out or update participant bios:
                            www.members.re-wrenches.org
                            
                          
                        
                        
                    
                  
                  
                _______________________________________________
                List sponsored by Redwood Alliance
                
                List Address: RE-wrenches at lists.re-wrenches.org
                
                Change listserver email address & settings:
                http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
                
                There are two list archives for searching. When
                  one doesn't work, try the other:
                https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
                http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
                
                List rules & etiquette:
                http://www.re-wrenches.org/etiquette.htm
                
                Check out or update participant bios:
                http://www.members.re-wrenches.org
                
              
            
          
          _______________________________________________
          List sponsored by Redwood Alliance
          
          List Address: RE-wrenches at lists.re-wrenches.org
          
          Change listserver email address & settings:
          http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
          
          There are two list archives for searching. When one doesn't
          work, try the other:
          https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
          http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
          
          List rules & etiquette:
          http://www.re-wrenches.org/etiquette.htm
          
          Check out or update participant bios:
          http://www.members.re-wrenches.org
          
        
      
      
      
      _______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


    
  

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201119/4b045f9e/attachment.htm>


More information about the RE-Wrenches mailing list