[RE-wrenches] Sol-Ark Gen Exercise Cycle
MDElectricSolar
mdelectricsolar at gmail.com
Fri Nov 13 14:43:56 EST 2020
Sol-Ark tech support has been fantastic to work with.
Mike
On Fri, Nov 13, 2020 at 9:09 AM Dustin Douglas <dustin at sol-ark.com> wrote:
> It is the same hardware as the dongle we provide with the unit and plugs
> directly into the Sol Ark Wi-fi port just like it would in a normal
> project, however the difference is that we customized the software to
> auto-update the inverter without the need for internet. This dongle is only
> compatible the Sol-Ark unit. We are currently sending them with the most up
> to date software for the units, but will be able to modify the software on
> the dongle so that it can be used for different versions of the Sol-Ark.
> The cost of the hardware is $100. We are wanting to add different options
> especially for those that are truly off grid.
>
> Thank you and have a blessed day,
>
> Dustin Douglas
>
> Sol Ark Engineering Support
>
> (972) 575-8875 x 108
> www.sol-ark.com
>
>
> ---- On Fri, 13 Nov 2020 10:05:37 -0600 *jay <jay.peltz at gmail.com
> <jay.peltz at gmail.com>>* wrote ----
>
> HI Dustin,
>
> Can you elaborate on the custom dongle for the non internet people. As
> its custom it sounds like its not a standard USB or SD or MSD?
>
> How much does it cost and can it be updated from a computer and then taken
> to the job site?
>
> Many if not most of my clients have no to limited internet and many that
> do, don’t want internet connection for their equipment.
>
> thanks
>
> Jay
>
> Peltz Power
>
>
>
>
>
>
>
> On Nov 13, 2020, at 8:57 AM, Dustin Douglas <dustin at sol-ark.com> wrote:
>
> The Time of Use feature can support this request. I do understand that
> programming can be somewhat confusing in completely covering what you are
> wanting the generator can do. However, if you are wanting the generator to
> turn on only when the batteries are low and getting through the night then
> we can set the Time of Use to only turn on with specific hours and also
> charge up to specific SOC. We implemented this setting so that there is the
> ability to control how much fuel is used and not run the gen for long
> periods of time. The Time of Use settings are very customizable, if you
> would like to give our support team a call and we can help customize it to
> best fit your scenario.
>
> As for updating the system itself, we offer different avenues of doing so.
> The first is the Wi-fi dongle that is connected to the inverter and to the
> customers home network. We also offer different aftermarket versions for
> customers with specific needs or if they don't have internet altogether.
> There is a ethernet version for those that don't want the over the air
> (OTA) connection to there wireless network or possibly if there router
> itself is a little to far away from where the unit is located. Simply
> running a ethernet cable to this specific dongle will connect them for
> monitoring and also allow for updates. The final version is for those true
> off grid installs where they are not worried about monitoring but do need
> to get the system updated. We have developed a custom design dongle that
> once inserted into the unit will perform the update on the inverter
> locally. Plug it in and wait for the final part of the software to finish
> and now your system will have the current version of software. You can then
> remove it and adjust the settings for the new features that were added.
>
> Thank you and have a blessed day,
> Dustin Douglas
> Sol Ark Engineering Support
> (972) 575-8875 x 108
> www.sol-ark.com
>
>
> ---- On Fri, 13 Nov 2020 08:46:31 -0600 *Jay <jay.peltz at gmail.com
> <jay.peltz at gmail.com>>* wrote ----
>
> I’m wondering how the firmware is updated? USB or other? I’ve looked on
> the website but I couldn’t find any instructions.
>
> Thx
> Jay
>
>
>
> On Nov 12, 2020, at 7:58 PM, Jeff Clearwater <jeffc at villagepowerdesign.com>
> wrote:
>
> Thanks Dustin for keeping us up to date on Sol-Arks feature progress.
>
> While you are upgrading your firmware: :)
>
> So an essential feature for off-grid with a generator is to be able to
> program various SOC levels for generator start AND shuf-off after charge.
> 90% is way too high for many sunny climes and other configurations. Often
> batteries need a boost in the wee morning hours - when they drop below the
> preferred recharge point but that's only perhaps a few hours before the sun
> comes up - So say you want to start a gen to charge a Lead-acid battery at
> 50% or an LFP batter at 20% SOC but you only want to bring it through to
> the next often or possibly sunny morning. So you set it to run from 50% to
> 65% (or from 20%-40% for LFP) - knowing that the morning sun will take it
> the rest of the way. 90% would waste a ton of fuel in this scenario not
> too mention unwanted noise and wear and tear on the genny. Depending on
> the clients use profile, the climate, and relative size of the array and
> battery and gen, these figures could vary anywhere from 20% to 100%. So
> it's essential us off-grid installers have that flexibility.
>
> Also I know that your TOU settings might cover this (though not in all
> modes I believe) but another nice feature is to have 2 or 3 time periods
> with different start and stop settings (Sunny Island does this nicely). So
> if the minimum SOC is reached in the evening you might as well bring it up
> to a higher SOC for gen shut down as it needs to get through the entire
> night whereas if that minimum SOC start trigger is met after 3 AM it needs
> to only bring it to a lower SOC as described above.
>
> I'm loving the Sol-Ark product so far but it is obvious the software is a
> work in progress - the architecture and thought behind it is an excellent
> foundation - thanks for your work and openness for input to make it even
> better.
>
> Best,
>
> Jeff
>
> ~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
> www.villagepowerdesign.com
> cell - 413-559-9763
> ~~~~~~~~~~~~~~~~~~~~~~~
>
>
>
> Dustin Douglas <dustin at sol-ark.com>
> November 12, 2020 at 11:46 AM
> Hi All,
>
> First and foremost thank you for sharing your experiences the the Sol-Ark
> system. We try very hard to have different capabilities and add new
> features that make it flexible for the customer. The two-wire start is a
> feature however that we want to be seamless. In the instance where the
> customer is seeing the system shutdown once the generator shuts off has
> been addressed and fixed with a software update. With this update we are
> able to handle larger generators that tend to drift from 60hz. Please give
> our support team a call so that we can update the customer accordingly. We
> are also looking at adding more features including the ability exercise the
> generator in the near feature.
>
> Thank you and have a blessed day,
> Dustin Douglas
> Sol Ark Engineering Support
> (972) 575-8875 x 108
> www.sol-ark.com
>
>
> ---- On Thu, 12 Nov 2020 08:08:51 -0600 *Jay <jay.peltz at gmail.com>
> <jay.peltz at gmail.com>* wrote ----
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> Jay <jay.peltz at gmail.com>
> November 12, 2020 at 9:08 AM
> Hi Bill
>
> In the past I’ve had similar issues with generators/inverters. Usually a
> relay on the output power wires that opens( disconnects) when the stop
> signal is sent works as the frequency doesn’t slowly go down, it drops to 0
> instantly.
> I don’t know if it will fix your issue.
>
> Seems like solark needs to greatly improve their firmware.
>
> Jay
>
> Peltz power.
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> Bill Hennessy <bill at berkssolar.com>
> November 11, 2020 at 10:03 PM
> Hi folks--We've also been disappointed with the Sol-Ark two-wire generator
> start. The unit starts at the charge set point, but the inverter will shut
> down for about a minute every time the generator stops running. After the
> minute wait, the inverter restarts and everything is fine. But it is
> aggravating for the homeowners to be left wondering in the dark.
>
> Sol-Ark says that when the generator shuts off, the frequency drops out of
> the Sol-Ark range and causes the inverter shut down.
> They suggested we find a way to increase the generator speed to avoid the
> frequency drop at shutdown. This seems like a lame suggestion, since the
> generator has no idea of when the batteries will be satisfied--it only
> responds to the on/off signal from the Sol-Ark. I would think that the unit
> could be programmed to ignore the frequency drop when it sends the shut off
> signal to the generator. The system has an an Ecogen 15kW.
>
> Not having an exercise function is also a miss. As mentioned below, the
> time of use can be used, but one has to go out and play with the
> programming to check the generator.
>
> regards, bill
>
> Bill Hennessy
> Berks Solar, LLC
> 371 Centennial Rd
> Mertztown, PA 19539
>
> o 610 682 4300
> c 484 560 4666
> NABCEP certified installer
> PA contractor #44411
> www.berkssolar.com
>
>
> On Wednesday, November 11, 2020, 8:20:57 PM EST, Chris Sparadeo
> <sparadeo.chris at gmail.com> <sparadeo.chris at gmail.com> wrote:
>
>
> Thanks for the suggestion, Jay.
>
> Yes, the Sol-Ark has a very basic and limited AGS for 2 wire compatible
> gen sets. Gen start can be programmed with voltage or SOC, however gen stop
> is not a function that can not be readily programmed. Instead, the Sol-Ark
> is programmed to charge the battery bank to 90% of the rated Ah capacity
> of the battery bank before turning off the generator. You can ultimately
> adjust this gen stop parameter to be based on a specific SOC or voltage,
> but I believe that doing so requires a call into tech support. The tech I
> spoke with updated a setting (having to do with a TOU parameter I believe)
> that was not accessible via the system interface. AGS from Schnieder,
> Outback and even Magnum are less clunky, but I am hoping that Sol-Ark will
> eventually come out with new programming to remediate these minor but
> nevertheless, important issues
>
> -Chris
>
> On Wed, Nov 11, 2020 at 3:58 PM Jay <jay.peltz at gmail.com> wrote:
>
>
> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Michael D Nelson
MD Electric & Solar Inc.
Office: 707-884-1862
Cell: 707-684-0064
www.mdelectricsolar.com
www.facebook.com/mdelectricandsolar
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201113/861b35be/attachment.htm>
More information about the RE-Wrenches
mailing list