[RE-wrenches] NEC 2020 - 705.12(B)(6)

William Miller william at millersolar.com
Mon Nov 9 12:48:53 EST 2020


. Where would 300A of current ever flow?



What is someone dropped a wrench on the bus?  It would fault with greater
than 200 amps.  This is and has been the point behind this code section.



William

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Jason Szumlanski
*Sent:* Sunday, November 8, 2020 9:47 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] NEC 2020 - 705.12(B)(6)



It's a 200A bus.



300A "on" the bus doesn't matter. The total of all load and supply devices
does not exceed the bus rating. This is 705.12(D)(2)(3)(c) in 2014/2017.



In no way can the total ampacity on the 200A bus exceed 200A as long as
additional loads are not added, hence the required warning label



On Sun, Nov 8, 2020, 12:30 PM Jay <jay.peltz at gmail.com> wrote:

Hi Jason



My question is if it’s 200a in from the main breaker and 100a from PV its
300 amps on the buss correct?



How is that ok with the 125% rule?



Or is this covered by some other rule as it’s a feed through lug load
center?



Jay







On Nov 8, 2020, at 9:46 AM, Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:



Maybe this is a better example (attached). I don't see how this would be a
problem under NEC 2014, 2017, or 2020. No portion of the main bus, feeder
conductors, or subpanel could possibly be subjected to overcurrent without
an OCPD stopping it.



My point is that here we are, 3 code cycles in since feeder taps were
addressed, and there is still no clarification of intent. AHJs are still
struggling with this.



I'm not sure where residential meter/mains with feed through lugs are
popular. I know they are in Florida and I have heard Hawaii. I'm curious
what your jurisdictions think of this if you have this scenario. Most of
the time the subpanel is main lug only, but adding a main circuit breaker
is usually an easy and cost-effective fix to make this interconnection type
work.



Jason Szumlanski











On Wed, Oct 28, 2020 at 5:15 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:

For further discussion, I don't see how my original scenario is any
different from this attached scenario, which I think everyone would agree
is allowed. All conductors and busbars are subject to the same potential
loads and fault currents.

 (Image attached).







On Wed, Oct 28, 2020 at 5:01 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:

Of course the feeder conductors and bus bar could be subjected to a fault.
But we're not talking about faults here. Fault protection is the job of the
PV OCPD And primary supply OCPD to protect the downstream busbar and
feeders. If that wasn't the case, you would need a new OCPD on BOTH the
load and line side of a solar connection as a feeder tap, not just the load
side.



If your interpretation is correct regarding the location of the OCPD, that
sounds like a sub-feed breaker is the only way to comply, and I haven't
seen such an animal for a typical residential load center. You can get
these for NQ panelboards and similar panelboards from other manufacturers
of course. It doesn't say as close as practicable or anything like that. It
says that a busbar connection is allowed when there are feeder CONDUCTORS
connected to feed through LUGS. What does "overcurrent device .. *at* the
supply end" mean? I emphasize "at." It's unclear how you would implement
this other than a sub-feed breaker I suppose, but that's not what it says.
It refers to feeder conductors on lugs on busbars, not feeder conductors on
load-side terminals of an overcurrent device.



My point is that 705.12 should have been wrapped up neatly in a bow, but
the lack of clarity, still, is astonishing. Why add a section about
feed-through lugs if it's going to be so vague?



Jason









On Wed, Oct 28, 2020 at 3:37 PM Brian Mehalic <brian at solarenergy.org> wrote:

Hey Jason,

Here's the 2020 text:



6) Connections shall be permitted on busbars of panelboards that supply
lugs connected to feed-through conductors. The feed-through conductors
shall be sized in accordance with 705.12(B)(1). Where an overcurrent device
is installed at the supply end of the feed-through conductors, the busbar
in the supplying panelboard shall be permitted to be sized in accordance
with 705.12(B)⁠(3)⁠(1) through 705.12(B)(3)(3).



The OCPD on the supply end of the feed-through conductors would be in the
form of a sub-feed breaker at the point of supply to those conductors,
re-establishing overcurrent protection of the conductors (likely at the
same ampacity as the main breaker in the supplying panel.  The feed-through
conductors are basically an extension of the busbar in the supplying panel;
they can either be protected by the main, or in the presence of multiple
sources of power in the supplying panel (such as a backfed PV system
breaker) they can be protected based on (B)(3)(1) - "the 125% rule" - or
they can be protected by a new overcurrent device at their point of supply,
in which case current on them is limited based on that OCPD size; in this
latter scenario the busbar in the supplying panel is allowed to be sized
based on one of (B)(3)(1) - (3) because it is protected downstream at its
end.



The theory is pretty much the same as 705.12(B)(1) for feeders - when not
connecting at the end of the feeder, use the "125% rule" or re-establish
overcurrent protection for that portion of the feeder subject to multiple
power sources.



In your drawing the 200 A feeder conductors, as well as the busbar below
the PV system breaker, could be subject to > 200 A in the event of a fault
somewhere along those conductors.



Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59

National Electrical Code® CMP-4 Member

(520) 204-6639



Solar Energy International
http://www.solarenergy.org
<https://mailtrack.io/trace/link/b21acbbeee09b823ad85f3914f3c4e6948b3ed61?url=http%3A%2F%2Fwww.solarenergy.org&userId=1613865&signature=8ec85587a9fbe44e>



SEI Professional Services

http://www.seisolarpros.com
<https://mailtrack.io/trace/link/16ff4b9d2b5a9ff30e778067c7a9f70657f436ad?url=http%3A%2F%2Fwww.seisolarpros.com&userId=1613865&signature=c8818c380f4375fb>







On Wed, Oct 28, 2020 at 10:18 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:

Does anyone else think they botched the wording in this section? It's still
not clear, and we have a ton of meter/main combos with feed-through lugs
around here.



Where is it written, "where an overcurrent device is installed at the *supply
end* of the feed-through conductors," (emphasis added) are they referring
to the solar backfed breaker on the busbar or another breaker somewhere
along the feeder circuit? It goes on to state that the loads on the
supplying busbar can comply with any method in 705.12(B)(3), which
prescribes an OCPD at the load end of the feeder in 705.12(B)(3)(3), so
they can't be talking about that. I have to assume it is the solar
backfed breaker they are referencing.



See my interpretation of one scenario in the attached image.



We're a long way off from the 2020 code implementation here, but it can
help sway plans examiners looking to clarify the intent of the 2014/2017
code cycles.





Jason Szumlanski

*Error! Filename not specified.*

*Error! Filename not specified.*

<Feed Through Lug Interconnection Option (2).pdf>

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201109/d4da906e/attachment.htm>


More information about the RE-Wrenches mailing list