[RE-wrenches] Bi-facial Open Circuit voltage testing

Jason Kechijian solarj at me.com
Tue Nov 3 15:18:06 EST 2020


Hey Brian,

Following up on both sets of questions:

Can you attach the spec sheet? Does it show curves at different irradiances? — ATTACHED

What was the time of day (or was it just cloudy?). — ~11:00am

How are you measuring the cell temp? — Fluke Temp gun (new battery)

The string voltages were +/- 1.5% of adjacent

Meter — Hioki CM4374 (calibrated recently)

Testing a single module, while ideal, is not practical unless we run into issues. I should have the ~480 strings worth of measured data back later today.


> On Nov 3, 2020, at 2:52 PM, Brian Mehalic <brian at solarenergy.org> wrote:
> 
> Hey Jason, IEC 62446-1 allows for:
> 
> Testing Voc of a single module and using that to calc the target string voltage
> and
> "For systems with multiple identical strings and where there is stable irradiance conditions, voltages between strings can be compared"
> 
> Regardless, it would be interesting to have a test on a single mod (well some number of single mods).
> 
> What meter are you using, and has it been calibrated recently?
> 
> 
> Brian Mehalic 
> NABCEP Certified Solar PV Installation Professional™ R031508-59
> National Electrical Code® CMP-4 Member
> (520) 204-6639
> 
> Solar Energy International
> http://www.solarenergy.org <http://www.solarenergy.org/>
> 
> SEI Professional Services
> http://www.seisolarpros.com <http://www.seisolarpros.com/>
> 
> 
> 
> On Tue, Nov 3, 2020 at 10:32 AM Brian Mehalic <brian at solarenergy.org <mailto:brian at solarenergy.org>> wrote:
> A few more questions:
> 
> Can you attach the spec sheet? Does it show curves at different irradiances?
> 
> What was the time of day (or was it just cloudy?). 
> 
> How are you measuring the cell temp?
> 
> Brian
> 
> > On Nov 3, 2020, at 8:50 AM, Jason Kechijian <solarj at me.com <mailto:solarj at me.com>> wrote:
> > Hey Jay and Brian,
> > 
> > System: 2p SAT
> > Mods/String: 27
> > 
> > Measurements taken on average of CB
> > Ambient: ~23ºC
> > Module: 21.4ºC
> > Wind: moderate
> > Irradiance: 500W/m2
> > 
> > Expected Voc: 1,320.37
> > 
> > Testing based on IEC 62446
> > Measured Voc on a range of 9 string combiner: 1251 - 1271. 1251 being the only string in the CB at less than 5% of expected, which I am sure the wind had some effects. All voltages in the CB were +/- 1.5% of the adjacent.
> > 
> > I’ll share more results as the come in from the field. 
> > 
> > The questions:
> > Which of the two Vocs should we use? The average of the two?
> > Since we are not taking the BOM temp measurements from a back sheet, but rather a cell. What does the thermal effect of glass play on the temperature reading vs. the back sheet. (May be wording this wrong, but I think y’all get the point)
> > 
> > I have searched the inter webs and not found much guidance/support in particular to this query.
> > 
> > 
> > Jason Kechijian
> > 
> > 
> >> 
> >> 
> >> Hey wrenches,
> >> 
> >> Does anyone have any guidance to which values to use when testing open circuit voltage on bi-facial modules, considering you take the temperature reading from the cell vs. the back sheet? Also, what would be the correct module Voc to use since there are values for both the front and back?
> >> 
> >> 405W Module: Front/Back
> >> Pmpp: 405 / 285
> >> Vmpp: 40.89 / 41.10
> >> Impp: 9.91 / 6.94
> >> Voc: 48.42 / 46.99
> >> Isc: 10.38 / 7.28
> >> Module efficiency: 19.7% / 13.9% 
> >> Temp coefficient Pmpp: -0.3528%/?C
> >> Temp coefficient Isc: +0.0400%/?C
> >> Temp coefficient Voc: -0.2769%/?C
> >> Nominal: 44+/-2?C
> >> 
> >> I was using the front Voc and Voc temp coefficient, but I am getting some results which are not in line with the 5% of expected.
> >> 
> >> Jason D. Kechijian, LEED AP
> >> NABCEP Certified PV Installation Professional?
> >> 
> >> 
> >> 
> >> 
> >> 
> >> ------------------------------
> >> 
> >> Message: 2
> >> Date: Mon, 2 Nov 2020 08:25:20 -0700
> >> From: Jay <jay.peltz at gmail.com <mailto:jay.peltz at gmail.com>>
> >> To: RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>>
> >> Subject: Re: [RE-wrenches] Bi-facial Open Circuit voltage testing
> >> Message-ID: <50543918-A062-456F-AC6D-6970C793F71A at gmail.com <mailto:50543918-A062-456F-AC6D-6970C793F71A at gmail.com>>
> >> Content-Type: text/plain; charset=utf-8
> >> 
> >> Hi Jason,
> >> 
> >> What are you seeing in terms of measurements?
> >> 
> >> Temp air/module 
> >> Voc
> >> Irradiance
> >> Etc
> >> 
> >> Jay
> >> Peltz power
> >> 
> >> 
> >> Message: 3
> >> Date: Mon, 02 Nov 2020 08:41:21 -0800
> >> From: Dave Angelini Offgrid Solar <offgridsolar at sti.net <mailto:offgridsolar at sti.net>>
> >> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>>
> >> Subject: Re: [RE-wrenches] Bi-facial Open Circuit voltage testing
> >> Message-ID: <4af9d868a899895ed1fd8ad15ba0ff2e at 127.0.0.1 <mailto:4af9d868a899895ed1fd8ad15ba0ff2e at 127.0.0.1>>
> >> Content-Type: text/plain; charset=UTF-8
> >> 
> >> I am curious why you care?  Is it close to maxing out cold weather Voc for
> >> one more panel in the string? If so I would be conservative and use one
> >> less panel.
> >> 
> >> I have an old Sanyo Bi Array and it pretty much has never gone outside the
> >> cold weather Voc that is logged by the controller. The 600v mppt just
> >> cranks out the power when the snow is off the array. It does pretty well
> >> also when the snow is on it. 
> >> 
> >> Just curious what you are doing? Testing used panels to make sure they are
> >> good? If so I would line them all up exactly the same and have a second set
> >> of eyes to record it all.
> >> 
> >> 
> >> Dave Angelini Offgrid Solar
> >> "we go where powerlines don't"
> >> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> >> e-mail offgridsolar at sti.net <mailto:offgridsolar at sti.net>
> >> text 209 813 0060
> >> 
> >> 
> >> ------------------------------
> >> 
> >> Message: 4
> >> Date: Mon, 2 Nov 2020 09:53:43 -0700
> >> From: Brian Mehalic <brian at solarenergy.org <mailto:brian at solarenergy.org>>
> >> To: RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>>
> >> Subject: Re: [RE-wrenches] Bi-facial Open Circuit voltage testing
> >> Message-ID:
> >>    <CAPKGs9Tz6yeHzWeOarDp0MVaMHuxMFhcLUoPROwEtXYNeW04gQ at mail.gmail.com <mailto:CAPKGs9Tz6yeHzWeOarDp0MVaMHuxMFhcLUoPROwEtXYNeW04gQ at mail.gmail.com>>
> >> Content-Type: text/plain; charset="utf-8"
> >> 
> >> I second Jay's request for some numbers, I'm curious about this not having
> >> participated directly in any bifacial projects yet.  The difference in Voc
> >> and Vmp ratios is interesting.
> >> 
> >> Brian Mehalic
> >> NABCEP Certified Solar PV Installation Professional? R031508-59
> >> National Electrical Code? CMP-4 Member
> >> (520) 204-6639
> >> 
> >> Solar Energy International
> >> http://www.solarenergy.org <http://www.solarenergy.org/>
> >> 
> >> SEI Professional Services
> >> http://www.seisolarpros.com <http://www.seisolarpros.com/>
> >> 
> >> 
> >> 
> >>> On Mon, Nov 2, 2020 at 8:55 AM Jay <jay.peltz at gmail.com <mailto:jay.peltz at gmail.com>> wrote:
> >>> Hi Jason,
> >>> What are you seeing in terms of measurements?
> >>> Temp air/module
> >>> Voc
> >>> Irradiance
> >>> Etc
> >>> Jay
> >>> Peltz power
> >>>> On Nov 2, 2020, at 8:18 AM, Jason Kechijian <solarj at me.com <mailto:solarj at me.com>> wrote:
> >>>> ?Hey wrenches,
> >>>> Does anyone have any guidance to which values to use when testing open
> >>> circuit voltage on bi-facial modules, considering you take the temperature
> >>> reading from the cell vs. the back sheet? Also, what would be the correct
> >>> module Voc to use since there are values for both the front and back?
> >>>> 405W Module: Front/Back
> >>>> Pmpp: 405 / 285
> >>>> Vmpp: 40.89 / 41.10
> >>>> Impp: 9.91 / 6.94
> >>>> Voc: 48.42 / 46.99
> >>>> Isc: 10.38 / 7.28
> >>>> Module efficiency: 19.7% / 13.9%
> >>>> Temp coefficient Pmpp: -0.3528%/?C
> >>>> Temp coefficient Isc: +0.0400%/?C
> >>>> Temp coefficient Voc: -0.2769%/?C
> >>>> Nominal: 44+/-2?C
> >>>> I was using the front Voc and Voc temp coefficient, but I am getting
> >>> some results which are not in line with the 5% of expected.
> >>>> Jason D. Kechijian, LEED AP
> >>>> NABCEP Certified PV Installation Professional?
> >>>> _______________________________________________
> >>>> List sponsored by Redwood Alliance
> >>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> >>>> Change listserver email address & settings:
> >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> >>>> There are two list archives for searching. When one doesn't work, try
> >>> the other:
> >>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> >>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> >>>> List rules & etiquette:
> >>>> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> >>>> Check out or update participant bios:
> >>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> >>> _______________________________________________
> >>> List sponsored by Redwood Alliance
> >>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> >>> Change listserver email address & settings:
> >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> >>> There are two list archives for searching. When one doesn't work, try the
> >>> other:
> >>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> >>> List rules & etiquette:
> >>> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> >>> Check out or update participant bios:
> >>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> >> -------------- next part --------------
> >> An HTML attachment was scrubbed...
> >> URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20201102/013a4e3f/attachment-0001.html <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20201102/013a4e3f/attachment-0001.html>>
> >> 
> >> ------------------------------
> >> 
> >> Subject: Digest Footer
> >> 
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >> 
> >> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> >> 
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> >> 
> >> There are two list archives for searching. When one doesn't work, try the other:
> >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> >> 
> >> List rules & etiquette:
> >> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> >> 
> >> Check out or update participant bios:
> >> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> >> 
> >> 
> >> 
> >> ------------------------------
> >> 
> >> End of RE-wrenches Digest, Vol 13, Issue 367
> >> ********************************************
> > 
> > _______________________________________________
> > List sponsored by Redwood Alliance
> > 
> > List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> > 
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> > 
> > There are two list archives for searching. When one doesn't work, try the other:
> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> > 
> > List rules & etiquette:
> > http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> > 
> > Check out or update participant bios:
> > http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201103/ce7aa13a/attachment.htm>


More information about the RE-Wrenches mailing list