[RE-wrenches] NEC 2020 - 705.12(B)(6)
Jason Szumlanski
jason at floridasolardesigngroup.com
Wed Oct 28 17:15:03 EDT 2020
For further discussion, I don't see how my original scenario is any
different from this attached scenario, which I think everyone would agree
is allowed. All conductors and busbars are subject to the same potential
loads and fault currents.
(Image attached).
On Wed, Oct 28, 2020 at 5:01 PM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
> Of course the feeder conductors and bus bar could be subjected to a fault.
> But we're not talking about faults here. Fault protection is the job of the
> PV OCPD And primary supply OCPD to protect the downstream busbar and
> feeders. If that wasn't the case, you would need a new OCPD on BOTH the
> load and line side of a solar connection as a feeder tap, not just the load
> side.
>
> If your interpretation is correct regarding the location of the OCPD, that
> sounds like a sub-feed breaker is the only way to comply, and I haven't
> seen such an animal for a typical residential load center. You can get
> these for NQ panelboards and similar panelboards from other manufacturers
> of course. It doesn't say as close as practicable or anything like that. It
> says that a busbar connection is allowed when there are feeder CONDUCTORS
> connected to feed through LUGS. What does "overcurrent device .. *at* the
> supply end" mean? I emphasize "at." It's unclear how you would implement
> this other than a sub-feed breaker I suppose, but that's not what it says.
> It refers to feeder conductors on lugs on busbars, not feeder conductors on
> load-side terminals of an overcurrent device.
>
> My point is that 705.12 should have been wrapped up neatly in a bow, but
> the lack of clarity, still, is astonishing. Why add a section about
> feed-through lugs if it's going to be so vague?
>
> Jason
>
>
>
>
> On Wed, Oct 28, 2020 at 3:37 PM Brian Mehalic <brian at solarenergy.org>
> wrote:
>
>> Hey Jason,
>> Here's the 2020 text:
>>
>> 6) Connections shall be permitted on busbars of panelboards that supply
>> lugs connected to feed-through conductors. The feed-through conductors
>> shall be sized in accordance with 705.12(B)(1). Where an overcurrent device
>> is installed at the supply end of the feed-through conductors, the busbar
>> in the supplying panelboard shall be permitted to be sized in accordance
>> with 705.12(B)(3)(1) through 705.12(B)(3)(3).
>>
>>
>> The OCPD on the supply end of the feed-through conductors would be in the
>> form of a sub-feed breaker at the point of supply to those conductors,
>> re-establishing overcurrent protection of the conductors (likely at the
>> same ampacity as the main breaker in the supplying panel. The feed-through
>> conductors are basically an extension of the busbar in the supplying panel;
>> they can either be protected by the main, or in the presence of multiple
>> sources of power in the supplying panel (such as a backfed PV system
>> breaker) they can be protected based on (B)(3)(1) - "the 125% rule" - or
>> they can be protected by a new overcurrent device at their point of supply,
>> in which case current on them is limited based on that OCPD size; in this
>> latter scenario the busbar in the supplying panel is allowed to be sized
>> based on one of (B)(3)(1) - (3) because it is protected downstream at its
>> end.
>>
>> The theory is pretty much the same as 705.12(B)(1) for feeders - when not
>> connecting at the end of the feeder, use the "125% rule" or re-establish
>> overcurrent protection for that portion of the feeder subject to multiple
>> power sources.
>>
>> In your drawing the 200 A feeder conductors, as well as the busbar below
>> the PV system breaker, could be subject to > 200 A in the event of a fault
>> somewhere along those conductors.
>>
>> Brian Mehalic
>> NABCEP Certified Solar PV Installation Professional™ R031508-59
>> National Electrical Code® CMP-4 Member
>> (520) 204-6639
>>
>> Solar Energy International
>> http://www.solarenergy.org
>> <https://mailtrack.io/trace/link/6861d7d8805b342c05a1945424d5d3679153b6c2?url=http%3A%2F%2Fwww.solarenergy.org&userId=1613865&signature=755f4d3125876434>
>>
>> SEI Professional Services
>> http://www.seisolarpros.com
>> <https://mailtrack.io/trace/link/56a599fdf28222e003dcf7711461480ee5165051?url=http%3A%2F%2Fwww.seisolarpros.com&userId=1613865&signature=68c217cadacd349b>
>>
>>
>>
>> On Wed, Oct 28, 2020 at 10:18 AM Jason Szumlanski <
>> jason at floridasolardesigngroup.com> wrote:
>>
>>> Does anyone else think they botched the wording in this section? It's
>>> still not clear, and we have a ton of meter/main combos with feed-through
>>> lugs around here.
>>>
>>> Where is it written, "where an overcurrent device is installed at the *supply
>>> end* of the feed-through conductors," (emphasis added) are they
>>> referring to the solar backfed breaker on the busbar or another breaker
>>> somewhere along the feeder circuit? It goes on to state that the loads on
>>> the supplying busbar can comply with any method in 705.12(B)(3), which
>>> prescribes an OCPD at the load end of the feeder in 705.12(B)(3)(3), so
>>> they can't be talking about that. I have to assume it is the solar
>>> backfed breaker they are referencing.
>>>
>>> See my interpretation of one scenario in the attached image.
>>>
>>> We're a long way off from the 2020 code implementation here, but it can
>>> help sway plans examiners looking to clarify the intent of the 2014/2017
>>> code cycles.
>>>
>>>
>>> Jason Szumlanski
>>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201028/e82496ae/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Screen Shot 2020-10-28 at 5.13.11 PM.jpg
Type: image/jpeg
Size: 71616 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201028/e82496ae/attachment.jpg>
More information about the RE-Wrenches
mailing list