[RE-wrenches] NEC 2020 - 705.12(B)(6)

Brian Mehalic brian at solarenergy.org
Wed Oct 28 15:36:41 EDT 2020


Hey Jason,
Here's the 2020 text:

6) Connections shall be permitted on busbars of panelboards that supply
lugs connected to feed-through conductors. The feed-through conductors
shall be sized in accordance with 705.12(B)(1). Where an overcurrent device
is installed at the supply end of the feed-through conductors, the busbar
in the supplying panelboard shall be permitted to be sized in accordance
with 705.12(B)⁠(3)⁠(1) through 705.12(B)(3)(3).


The OCPD on the supply end of the feed-through conductors would be in the
form of a sub-feed breaker at the point of supply to those conductors,
re-establishing overcurrent protection of the conductors (likely at the
same ampacity as the main breaker in the supplying panel.  The feed-through
conductors are basically an extension of the busbar in the supplying panel;
they can either be protected by the main, or in the presence of multiple
sources of power in the supplying panel (such as a backfed PV system
breaker) they can be protected based on (B)(3)(1) - "the 125% rule" - or
they can be protected by a new overcurrent device at their point of supply,
in which case current on them is limited based on that OCPD size; in this
latter scenario the busbar in the supplying panel is allowed to be sized
based on one of (B)(3)(1) - (3) because it is protected downstream at its
end.

The theory is pretty much the same as 705.12(B)(1) for feeders - when not
connecting at the end of the feeder, use the "125% rule" or re-establish
overcurrent protection for that portion of the feeder subject to multiple
power sources.

In your drawing the 200 A feeder conductors, as well as the busbar below
the PV system breaker, could be subject to > 200 A in the event of a fault
somewhere along those conductors.

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Wed, Oct 28, 2020 at 10:18 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:

> Does anyone else think they botched the wording in this section? It's
> still not clear, and we have a ton of meter/main combos with feed-through
> lugs around here.
>
> Where is it written, "where an overcurrent device is installed at the *supply
> end* of the feed-through conductors," (emphasis added) are they referring
> to the solar backfed breaker on the busbar or another breaker somewhere
> along the feeder circuit? It goes on to state that the loads on the
> supplying busbar can comply with any method in 705.12(B)(3), which
> prescribes an OCPD at the load end of the feeder in 705.12(B)(3)(3), so
> they can't be talking about that. I have to assume it is the solar
> backfed breaker they are referencing.
>
> See my interpretation of one scenario in the attached image.
>
> We're a long way off from the 2020 code implementation here, but it can
> help sway plans examiners looking to clarify the intent of the 2014/2017
> code cycles.
>
>
> Jason Szumlanski
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201028/6099c636/attachment.htm>


More information about the RE-Wrenches mailing list